Looking at the picture above what would be my options for adding a new 32amp radial circuit for an electric cooker? Would it be possible to run the circuit a short distance from the CU to a RCD FCU and then on to the cooker control unit? Or is that half a foot of unprotected (RCD) cable not acceptable? Only other option would be a new CU I guess? Or can you buy RCBO's that fit a CU this old?

Thanks
 
What your planning is within the regs. That short run from the cu to the new rcd FCU doesn't need rcd protection if its clipped direct. You could always use pvc conduit like the rest? Either way is fine.
 
Hi

View attachment 5722

Looking at the picture above what would be my options for adding a new 32amp radial circuit for an electric cooker? Would it be possible to run the circuit a short distance from the CU to a RCD FCU and then on to the cooker control unit? Or is that half a foot of unprotected (RCD) cable not acceptable? Only other option would be a new CU I guess? Or can you buy RCBO's that fit a CU this old?

Thanks

Is there not a cooker circuit already provided in this CU?? If so, why do you need another cooker point/FCU?? You haven't been to B&Q and listened to there crap about needing two supplies for a split load oven/hob installation, ....Have you???
 

Reply to New cooker radial circuit! in the Australia area at ElectriciansForums.net

Similar threads

  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
686

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top