Peter Woodford

Guys,

client is just moving into place and ordered new cooker curries have said he needs a 6mm 32 amp. I have suggest i run in a 10mm and still rate it at 32amp just incase they decide to upgrade to a double cooker again when they refurb the kitchen to save then money. Also has anyone got any ideas on getting the cable behind the wall unit and also taking some tiles off so i don't damage them. Want to do a really good job on this as there could be quiet a bit of other work there later on.Also can someone tell me were to find the chart on what a major and whats a minor is saw it the other day in one of my books but can't find it now. Am i right in thinking this is a major so will have to go on a full cert or is it covered under a minor works cert

thanks
 
If you`re putting in a new cct - or even re-routing old one, or altering ccc or cct protection, will require an EIC. Pretty obvious i`d have thought...

As to Curry`s advising on what cable to install - thats scary, laughable, & beyond their brief (also illegal)

Any idea of the cooker`s rating Peter?
 
the guy does'nt know this is the first thing i asked but he needs a price asap wants it done on sat not sure to price for 16mm thinking about it. did also say to him that could'nt take note of curries when do they know anything
 
Last edited by a moderator:

Reply to new cooker in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
687
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top