Hi

We are installing new parking barriers on existing couloured SWA (RED YELLOW BLUE). Do we sleeve the cores to the new colours (BROWN GREEN/YELLOW BLUE) or leave them as the old colours. As they wil be the old colours in the DB. :confused:
 
Leave it and apply the warning notice "This installation has wiring to 2 versions of BS7671 blah blah blah" at the DB.

Cheers.........Howard

PS cant remember the exact wording on the sticker, but there is only one and there is a piccy in the BRB and OSG.
 
Last edited by a moderator:
Thanks Howard,

If we have to adjust the length of the existing SWA and re gland do we sleeve the colours RED GREEN/YELLOW BLACK ?

Leave it and apply the warning notice "This installation has wiring to 2 versions of BS7671 blah blah blah" at the DB.

Cheers.........Howard

PS cant remember the exact wording on the sticker, but there is only one and there is a piccy in the BRB and OSG.
 
Thanks Howard,

If we have to adjust the length of the existing SWA and re gland do we sleeve the colours RED GREEN/YELLOW BLACK ?

No, just do as above, the warning notice covers it all with comments like ensure cables are correctly identified before doing this and that. It is no different to a domestic install where blue and brown are joined to red and black.

Cheers.........Howard
 

Reply to New equipment old colours in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Time to get an electrician.
    • Like
2 3
Replies
31
Views
3K
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top