Spotted today
Best practice guides : Electrical Safety Council
Lots of revisions compared to the previous edition, but mainly updating references and bring in new references to section 712 in 7671.
Already a bit overtaken by events because it says DTI Guide V3 is expected to be published in Autumn 2011 and it is not here yet.
One interesting bit is that it covers fitting microgeneration downstream of existing rcds which we have discussed here. It is relaxed about it provided the rcd is double pole. It has a diagram explaining why. However for pv I believe it would still not be allowed if the rcd was there for ADS rather than additional protection reasons (712.411.3.2.1.1).
Regards
Bruce
Best practice guides : Electrical Safety Council
Lots of revisions compared to the previous edition, but mainly updating references and bring in new references to section 712 in 7671.
Already a bit overtaken by events because it says DTI Guide V3 is expected to be published in Autumn 2011 and it is not here yet.
One interesting bit is that it covers fitting microgeneration downstream of existing rcds which we have discussed here. It is relaxed about it provided the rcd is double pole. It has a diagram explaining why. However for pv I believe it would still not be allowed if the rcd was there for ADS rather than additional protection reasons (712.411.3.2.1.1).
Regards
Bruce