Hello Guys,

I have a strange, yet accurate title: I am the Vintage Member for the WBCCI. That is the club for people who own Airstreams. (the aluminium bodied, curved caravan, or as we call them: A Travel Trailer) In my case, the Euro branch. This means that members who have problems come and ask me. There is a problem I've considered for a while.

Many importers of vintage Airstreams fit transformers in order to use the 110v system in the trailer. This is most often because the trailer may contain 110v appliances. A fridge or often an AirCon system. This means firing up the vintage wiring which is not generally a problem in itself. US wiring is very robust and bomb proof and will last for decades.

The problem I want to solve is fuses and particularly RCDs: The 110v side of transformer is not protected by the RCD which are fitted into the 240v input (this is typically via a small fusebox, the type of thing you would fit in a garage extension) The fuses which are fitted in the Airstreams are only MCBs and provide no protection to the system. How can I solve this?

Can we use UK fuses, such as a UK RCD inline on the 110v feed
 
Gentlemen,
I’m gratified by your assistance. I’ll go through your responses 1 at a time. Firstly, I use a toroidal transformer supplied by Airlink in Essex. Very reliable bomb-proof kit. I know of some people who have used the yellow site units. I warn them off strongly as they aren’t intended for continuous use. The 110v appliances work very well despite the reduce in Hertz rate from 60(US)to 50Hz in the UK.
I’m sure the trans is referenced to earth but not sure if it’s 55+55.
I have found a earth leakage circuit breaker on Amazon.com. Seems perfect as it protects to 30amp in a 3kva circuit but it’s single pole. Why does it need to be double pole?
 
Last edited:
The 110v appliances work very well despite the reduce in Hertz rate from 60(US)to 50Hz in the UK.
I’m sure the trans is referenced to earth but not sure if it’s 55+55.
I have found a earth leakage circuit breaker on Amazon.com. Seems perfect as it protects to 30amp in a 3kva circuit but it’s single pole. Why does it need to be double pole?

You need to find out if and how the secondary side of the transformer is earthed and the type of rcd required before sourcing the RCD.

If the output of the transformer is not referenced to earth then there is unlikely to be much point fitting an rcd at all.

Double pole fusing, mcbs and rcds will be needed if neither pole of the supply is referenced to earth or if it is centre tapped to earth as both conductors are line conductors.
Single pole devices are only suitable if there is only one line conductor.
 
You need to find out if and how the secondary side of the transformer is earthed and the type of rcd required before sourcing the RCD.

If the output of the transformer is not referenced to earth then there is unlikely to be much point fitting an rcd at all.

Double pole fusing, mcbs and rcds will be needed if neither pole of the supply is referenced to earth or if it is centre tapped to earth as both conductors are line conductors.
Single pole devices are only suitable if there is only one line conductor.

You've contradicted yourself in that post Dave.

Even if the secondary has no reference to earth, an RCD will still function if there is a current imbalance. Which there would be if someone grabbed a live conductor through capacitive coupling. Not sure if it's enough to divert 30mA but if it was, a functioning RCD would operate.

Seen a few setups in labs that use an isolated transformer, then have 5mA RCDs on the circuits.
 
You've contradicted yourself in that post Dave.

Even if the secondary has no reference to earth, an RCD will still function if there is a current imbalance. Which there would be if someone grabbed a live conductor through capacitive coupling. Not sure if it's enough to divert 30mA but if it was, a functioning RCD would operate.

Seen a few setups in labs that use an isolated transformer, then have 5mA RCDs on the circuits.

Have I? You'll have to give me a clue as I can't see it for ----?

Is that capacitive coupling between the windings of the transformer? Assuming the supply and outgoing wiring are physically seperate I can't see where else it could be coupled.
 
Have I? You'll have to give me a clue as I can't see it for ****?

Is that capacitive coupling between the windings of the transformer? Assuming the supply and outgoing wiring are physically seperate I can't see where else it could be coupled.

If the output of the transformer is not referenced to earth then there is unlikely to be much point fitting an rcd at all.

Double pole fusing, mcbs and rcds will be needed if neither pole of the supply is referenced to earth or if it is centre tapped

Reading again, I imagine its a typo and you meant either rather than neither.

Capacitive coupling through the human body.
 

Reply to New Fuse Box Needed for 110v Electrics in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top