M

mdgibbs32

Hi All
I have been asked to look into putting in a CU in a garage that is likely to be converted into a granny flat in the near future. Planning on using 10mm or 16mm SWA cable (buried to 600mm) as no real idea what load is going to be if it is converted so want to take worst case into consideration. Owner has said he is going to install gas heating but i cant guarantee that, or what shower is going to be used etc etc.
Plan on installing a small split load CU in garage but cant make my mind up whether to attache to existing CU in house or whether to split into the tails via henley block. All experianced advice gratefull received. Thanks
 
Depends on what the present supply in the house can safety allocate to this future granny flat. i can't see you needing more than a 10mm supply cable. i can't see a granny needing more than a 8KW shower, if gas isn't used for heating and water. Nothing stopping you in the first instance taking the supply from the existing CU for garage purposes, which can be changed to Henley blocks at a later date...
 
Hi All
I have been asked to look into putting in a CU in a garage that is likely to be converted into a granny flat in the near future. Planning on using 10mm or 16mm SWA cable (buried to 600mm) as no real idea what load is going to be if it is converted so want to take worst case into consideration. Owner has said he is going to install gas heating but i cant guarantee that, or what shower is going to be used etc etc.
Plan on installing a small split load CU in garage but cant make my mind up whether to attache to existing CU in house or whether to split into the tails via henley block. All experianced advice gratefull received. Thanks

if you do split the supply with the tails from henley blocks to the main consumer unit rather than feed the new dist board to the granny flat from the existing DB, don't forget you need to add a main switch, you need 1 main switch to isolate everything, and IMO for what it's worth here I would suggest a 10mm2 3 core armoured, I doubt a 16mm2 would be required for an area that small considering gas heating will be used, JMO.
 
Depends on what the present supply in the house can safety allocate to this future granny flat. i can't see you needing more than a 10mm supply cable. i can't see a granny needing more than a 8KW shower, if gas isn't used for heating and water. Nothing stopping you in the first instance taking the supply from the existing CU for garage purposes, which can be changed to Henley blocks at a later date...
i`d go for a 16mmCSA...and give em 60A....(depending on all the usualls of course..VD etc)....
 
Jesus, ....what are you expecting in this maybe granny flat/come garage to warrant a 60A supply?? The main house will probably only have an 80A to start with... lol!!
dont get me wrong here eng...i understand the issue you may have....
but you can protect the 16mm csa sub with 60A opd...you aint gonna get blowing bullits as you quite rightly say it will never get there......but use the fuse to protect the cable.....
 
dont get me wrong here eng...i understand the issue you may have....
but you can protect the 16mm csa sub with 60A opd...you aint gonna get blowing bullits as you quite rightly say it will never get there......but use the fuse to protect the cable.....

Sorry, i just don't understand your reasoning for a 16mm sub on a 60A supply for at best a granny flat.
 
i understand it may seem extreem....and as the O/P has stated it may be that a 10mmCSA is adequate...theres a few `maybe`s` goin on here...such as the KW rating of shower.....and the choice of leccy...or gas for water heating....
 
i understand it may seem extreem....and as the O/P has stated it may be that a 10mmCSA is adequate...theres a few `maybe`s` goin on here...such as the KW rating of shower.....and the choice of leccy...or gas for water heating....

Unless this garage is a good distance away from the main house, it just isn't going to warrant a 16mm cable and certainly not 60A supply. You'll be lucky to see 40A being drawn on a normal family 2 bed house 99% of the time, so for such a small area, for one person, It'll just be a total waste of time, hassle and money....
 

Reply to "new granny flat" in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...
Replies
9
Views
1K
  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top