Hi ! sorry seem to be flying questions out tonight, I do try and look honest....
So ...If i had a domestic property that had everything as newly installed in apart from a lighting circuit and a ring. would this be classed on cert as New instal addition or alteration, or ALL above....
And if there any issues with the old circuits that were kept that needed further investigation as not meeting reg's would i state that on EIC or/and on a accompany PIR for the old circuits put onto the new board.?
oh and the main earth conductor is 16mm from board going to a earth block which is then sized down to 10mm which goes into the suppliers main TNCS block......Can you commission an install with this or just note it? advise to contact proivder for earth MET upgrade.
So ...If i had a domestic property that had everything as newly installed in apart from a lighting circuit and a ring. would this be classed on cert as New instal addition or alteration, or ALL above....
And if there any issues with the old circuits that were kept that needed further investigation as not meeting reg's would i state that on EIC or/and on a accompany PIR for the old circuits put onto the new board.?
oh and the main earth conductor is 16mm from board going to a earth block which is then sized down to 10mm which goes into the suppliers main TNCS block......Can you commission an install with this or just note it? advise to contact proivder for earth MET upgrade.