Screed will be 100mm thick, and UFH pipes will be at the base of that and 15mm diameter. So no reason why you can chase down 50 - 70mm or so to accommodate new cables. Also with use of a thermal camera you may well be able to get between the UFH pipes.
 
Screed will be 100mm thick, and UFH pipes will be at the base of that and 15mm diameter. So no reason why you can chase down 50 - 70mm or so to accommodate new cables.
I've fitted plenty of wet UFH systems, and the screed is normally 60 - 65mm thick. The pipes are on the surface of this, so nominally the top of the pipes is about 45 - 50mm below the surface. I leave the pipes all carefully clipped down on the insulation, but after the builder's labourers have clomped all over in their size 12s with barrow loads of screed, I wouldn't guarantee anything more than 30mm.
I've also fitted UFH under chipboard floors, and in these cases the pipes are immediately under the board.
It would be a good idea to go for the kind of kitchen units that sits on exposed decorative legs, rather than those with kickboards.
 
Unless you have first hand knowledge of the specific building being discussed here how can you be so certain of this?
Good point...just going by personal experience on best practice having been through some renovation projects. However, thickness doesnt really matter as even if its as thin as, say, 50mm, with use of a thermal camera and careful grinding, it will be possible to create a channel to take some low profile conduit.
 
Good point...just going by personal experience on best practice having been through some renovation projects. However, thickness doesnt really matter as even if its as thin as, say, 50mm, with use of a thermal camera and careful grinding, it will be possible to create a channel to take some low profile conduit.

But you want to avoid having the cables in the heated screed otherwise you end up with much bigger cables.
 
Have you asked the person who did the underfloor heating if they have a picture of it before screeding?
It is a common think they do for multiple reasons. This would give you reference points.
I wouldn't vory about heat much as any competent sparky would figure that-one easily out...
 

Reply to New kitchen install over existing wet underfloor heating in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock