A friend of mine had a shower unit pack up,and had a spare shower unit from a previous house move.I went round to inspect the old unit which was a 10.5kw shower.I looked internally in unit to my surprise to see it fed by 4mm,i looked at the back wall of the shower wall to see how it was fed as it dangled from the ceiling with no clips or trunking via a DP switch.Obviously the previous cowboy found the cable short and decided to extend this by a switch.I further investigated the mcb size obviously concerned about overheating and to my surprise it was a 32amp mcb,so how on earth did it function when you would have logically thought it would have drawn at least 40amps????????.So would the 9.5kw shower (spare)realistically work,NOT THAT i would condone that sought of thing.As i would install to regs and manufacturers spec.The 4mm would be protected by the 32amp mcb which is adequate.
 
The load also varies from unit to unit, i.e some units have three or four seperate elements. These are controlled by a few things (again dependant on unit), temperature of incoming water/ temperature of outgoing water/ users chosen heat setting, etc. And as above, not many people shower longer than 15mins. Hope this helps.
 
In my opinion It's not a good idea running that cable at over 40 amps even on a 32 amp breaker,
like telectrix says it can take an hour to trip it, that cable will probably be in insulation and I can see the shower be used for one person after another, so that shower coud be on for quiet some time.
 
yep of course Will i did not want to complete this mess!!!as a matter of fact because the install looked so bad i checked the cable run in loft.There was 6" of insulation which brings me to two another confirmation's.Am i correct in saying that if a cable is clipped direct to the side of the joist then it negates the de-rating factor as this dissipates any heat.How do you guys size the difference between 4mm and 6mm visually.Apart from having small pieces with you to compare.I know this sounds a daft question but 2mm dif. needs a bionic eye.
 
Out of interest why are you working out of the BRB??? we are now on the BGB!
oh dear should i be tarred and feathered lol Why the hell should i fork out for forkin ÂŁ65.00+ when i can look at amendments.It beggars belief on here when some people nit pick!!!!!! this game is expensive enough changing books so quickly with amendments.To some degree its a money generating exercise
 
You need to look at the bgb, which is the current wiring regulations, we all go by it. A mcb ( circuit breaker ) will take more than its rated at for a set amount of time, their rated as a b c d . The graphs in the book of regulations will make it clear to you.
 
hi-- "just add water",in reply to your q- people at the top, writing regulations, need to keep their highly paid jobs! simple-
so-- they keep inventing - first the red then the green
what could be a better job!
a frigging yellow one next
then a mauve
 

Reply to new shower in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
244
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
717
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
686

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top