have a question....

started a barn conversion, first fix done... client contacted EDF so a new supply can be brought in and they are asking for a completed installation certificate before they bring a new cable in to supply new installation........!!! how can it be completed if there is no power to do the live testing....? confused dot com....!!!

BTW it's a TT system

nick
 
You can carry out an initial verification which will contain all of the dead tests. Then you can apply the 'enquired' ze to the readings for comparison.


It is quite common for suppliers to want to obtain an installation cert prior to their connection. Occasionally, it may be an existing PIR that is requested.
 
Last edited:
cheers widdler...

so.... apply Ze....and calculate the Zs's.....? how about the RCD times...?

do you know what exactly there want form the test sheets or is it just a matter of seeing them...?

there was no existing PIR it was an old barn that never had power.... nearest incoming supply is overhead power lines and i think the tap off tranny is about 40m away...
 

Reply to New Supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K
  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top