D

David Nicholls

Hi New to the Forum here.

I am a qualified Electrician however inexperienced due to spending 4 years in the army since finishing my apprenticeship. Trying my hardest to get back to the standard that I should be at. I have sat and passed the 17th edition but currently not got 2394/5. Plan to take this when ready and not before.

With regards to Main Bonding Conductors and supplementary bonding. I can find in the regs all the appropriate sizing tables etc but I'm really struggling to find any acceptable readings so that if I were to take an R2 measurement does it satisfy the regs.

Can any one point me in the right direction?

Thanks in advance!
 
measure your R2. then look up the mili ohms/m for that size cable. multiply by the approx length and if it's close to the measured value, then fine. a rule of thumb is 30m of 10mm will be approx.0.05 ohms
 
Hi New to the Forum here.

I am a qualified Electrician however inexperienced due to spending 4 years in the army since finishing my apprenticeship. Trying my hardest to get back to the standard that I should be at. I have sat and passed the 17th edition but currently not got 2394/5. Plan to take this when ready and not before.

With regards to Main Bonding Conductors and supplementary bonding. I can find in the regs all the appropriate sizing tables etc but I'm really struggling to find any acceptable readings so that if I were to take an R2 measurement does it satisfy the regs.

Can any one point me in the right direction?

Thanks in advance!

https://www.youtube.com/watch?v=rnvNfI__kYU
 

Reply to New to Forum. Main Bonding conductor r2 readings. in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
669
loz2754
L
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top