OK Pablo, had a good think about this.
All of the lights dim - this indicates a loss of voltage.
Now, lets suppose you have a damaged cable ANYWHERE in the house. Lets suppose that what you have is an intermiitent short between phase and neutral (due to damaged insulation etc)
When the short 'occurs' the result is that the voltage on your entire system would drop dramatically, as there momentarily the phase and neutral conductors would become 'electrically the same point' and there would be no potential difference (voltage) between them (this is all theoretically)
Now a TV for example, when on, could drop its supply to as low as about 50V without going off. The point i am making is that ALL of your house voltage could be dropping, but it would only be evident on the lighting circuit!
So lets say the fault is on the new wiring, under these circumstances it would still effect the exisiting house circuit.
So why the bang?
If the cables are 'just touching', then at a set point they will get close enough so that current will be able to jump the gap between them. this now a fault current which will rise very rapidly (hence the drop in voltage etc) however as it is a 'weak' path, then the bang is the cables 'blowing' themselves apart again.
you must appreciate this is all hypothetical. And because of the nature of your loads, and the current we are taking about, there will also be an elemant of collapsing magnetic fields (due to basically an inrush of current due to the fault) 'assisting' the spark which is essentially jumping between your cables.
I am trying my best to describe it, but if you ever seen a set of contacts opening on a circuit (like the old contact breaker points in earlier cars), well the spark you see is essentially whats happening in/around one of your cables/connections.
How do you find the problem?
Well if the circuit with the faulty cable is electrically isolated, then the fault wont occur. i.e. with your extension circuits off and you dont get the bang, then i would switch ONE of the cirucits back in (ring main) and observe....... then switch that off and put the lights back on and wait........
Now if you can identify the faulty circuit ( and assuming you do not have test equipment) ( and also assuming you have sufficient electrical knowledge to isolate circuits safely), then I would isolate ,say half the lighting circuit, and wait....
By a process of eleimination you should be able to identify WHICH cable is faulty. Of course, you really need a decent sparks on this - and the original ssparks may not be at fault - its amazing how much damage a nail can do AFTER the sparks has signed the job off
Of course, I could be talking out of my butt (been acused of that before!), but anyone got a better theory??!
Oh, and another thought. If my theory is coorect, it may be evident if you plug a table lamp into a socket and see if that dims at the same time as the house lights
Thank you for your time spent with your reply and also for putting it into language that i understand!!
I turned the tripswitches for the extension off to find out whether the noise is actually from the extension wiring and after hearing, what seemed like, a similar noise i got fed up and turned it back on again. There was some existing wiring that was terminated around the area of noise but i safely disconnected that but it made no improvement.
I ought to do this methodically, as you advise, and also be a little more patient!! Tomorrow i shall disconnect the extension once again and take things a little more slowly. At the moment I am sitting upstairs in the computer room with only a lamp turned on to see if mains is as affected as the lighting circuit but sod’s law – no bang!
We even got to the point of thinking that the noise could possibly be due to expansion and contraction of copper heating pipes. Reason being is that a long steel girder had to be placed touching some pipework where there was little other option (due to gap between ceiling downstairs and floor upstairs). But i guess that could be negated as there ‘shouldn't’ be any sort of voltage drop when this happens.
Just to mention, we have had an electrician to do some testing since the lounge was completely finished and he couldn’t find any source of the problem either.
My dad’s an engineer and might be able to get some sort of oscilliscope device to try over a weekend which he said is some kind of grid that you place over a surface and it peaks where the sound is eminating and you can further narrow it down by compressing the grid. I’m just guessing but maybe with that device and one of those electrical cable detectors….maybe a long shot!!
I was wondering whether there is any kind of monitoring equipment that you could connect into a socket or onto a light fitting which has a memory to see if there are any spikes occurring and can record the time. (A lot of guessing going on in this reply, but just thinking aloud!!)
Oh and another thought Pablo (been thinking again)
when you got electrical sparks you get localized ionisation of the air surrounding the spark. Essentially this means the air becomes electrically charged, and essenetially 'explodes' as the current iginties it.
I haver seen this with testing high voltage circuits with meters, if there is too much exposed conductor on the meter probe, as the probe gets close enough for the spark to jump, there is what can best be described as ' flash over' with a mini explosion.
If this is happening on your cable ( on a very small scale) it would account for the bang - and I have no doubt were you in a position to observe it, you would see a flash as well!!
Hehe! I hope it doesn’t come to ripping the walls off as we are quite pleased with the extension itself!!
@ Grae79:
Thanks for replying. Here is a little link to the relevant page of the installation certificate:
Pablo:-
Re the electrical problem you are experiencing,after some consideration,as Tony says voltage drop is the issue that causes your lights to dim.
Not entirely convinced that having all that load on those dimmers is good practice,due to heat build up etc.
I would recommend replacing the dimmers with normal rocker switches temporarily to see if this eliminates the 'noise' experienced.Not convinced that a short is being experienced since there is no mention of you having to reset the overcurrent protective device,when the 'explosion' occurs.
The theory i have with regards to voltage drop may be that your house may be on the same phase supplying another installation with high inrush currents,if you can establish which phase you are on,and compare that to other installations nearby,e.g. neighbours then by enquiry it may be known who is pulling the most load on a particular phase.
It may also help to try to establish a timeline for these events within your installation.
Thank you for your response too.
Everything works as it should. The only thing we experience is the light dimming very briefly before the ‘bang’ and that’s it. There is no resetting required after the ‘bang.’
You have got me thinking about the dimmers though. I listed the dimmers in the first post as 60-300W but after some research think that they are only 250W rated per gang. With the GU10 50W bulbs, I have been advised to double their wattage when calculating load on each gang on the dimmer. Meaning the sets of 4 spotlights should be treated as 400W load on their particular gang which is over the dimmer spec. I didn’t see this as a major issue as the noise also occurs in the middle of the night when all lounge lights are turned off. However, excusing my ignorance, is there some kind of residual load that exists when they are off?
Also we are on single phase. But again, as this can happen any time of the day, I would have thought it was unlikely to be affected by large neighbouring loads. Will also take your advice on noting times of occurrence.
Thank you all again for your replies. I will post back with results when I have results of isolation ‘testing’ as time and patience allows! Any more thoughts are welcomed.
Paul