Hi
New to trade and 1[SUP]st[/SUP] post – any help/advice appreciated
Testing DIY installation approx. 10 years old. Final circuit for sockets – a radial (not ring) wired in 2.5mm T&E protected by 20A mcb to BSEN 60898. Not logically wired, several JBs in loft and a number of spurs so not easy to identify “end” of circuit as cable runs all over place in loft backwards & forwards.
I make max Zs from OSG table B6 to be 1.85 ohms.
Using Megger 1720 only a few months old. Testing Zs with the Megger plug adaptor
Zs results confusing me so have tested at every socket in final circuit.
1) Zs varies in each double socket depending on if use LHS or RHS of double socket e.g. LHS 1.98 (fail) RHS 1.63 (pass). Is this to be expected and which reading do I take as proving 0.4 sec disconnection time?
2) Results vary in same room, some sockets pass & some fail. Should I be taking highest reading of complete circuit (several rooms) to show disconnection compliance?
3) Have located several JBs in loft & tightened the screw terminals. Retested every socket. All except 1 have increased Zs from original readings (the 1 decreased). I would have expected Zs to be lower with tighter connections. Can anyone explain why this could be happening?
Basically confused now as to what is going on and why. Any help/advice/pointers really appreciated
Thanks
Nige
New to trade and 1[SUP]st[/SUP] post – any help/advice appreciated
Testing DIY installation approx. 10 years old. Final circuit for sockets – a radial (not ring) wired in 2.5mm T&E protected by 20A mcb to BSEN 60898. Not logically wired, several JBs in loft and a number of spurs so not easy to identify “end” of circuit as cable runs all over place in loft backwards & forwards.
I make max Zs from OSG table B6 to be 1.85 ohms.
Using Megger 1720 only a few months old. Testing Zs with the Megger plug adaptor
Zs results confusing me so have tested at every socket in final circuit.
1) Zs varies in each double socket depending on if use LHS or RHS of double socket e.g. LHS 1.98 (fail) RHS 1.63 (pass). Is this to be expected and which reading do I take as proving 0.4 sec disconnection time?
2) Results vary in same room, some sockets pass & some fail. Should I be taking highest reading of complete circuit (several rooms) to show disconnection compliance?
3) Have located several JBs in loft & tightened the screw terminals. Retested every socket. All except 1 have increased Zs from original readings (the 1 decreased). I would have expected Zs to be lower with tighter connections. Can anyone explain why this could be happening?
Basically confused now as to what is going on and why. Any help/advice/pointers really appreciated
Thanks
Nige