T
tomchester999
Hello
I have my niceic competent person scheme visit next week.
I have done the consumer unit change (I am pretty sure about the tests - just do them all)
Few Questions-
1. The second job I've done is adding a new circuit (just an outside light on its own breaker)
What tests would I be expected to carry out on this one?
as I am adding a new circuit I need to do a whole electrical installation cert. do i just write in the new circuit?
2. The first job is a TT system, what electrode test am I supposed to carry out. ? I have done the prospective earth fault current and got 280ohms, it says in the osg it should always be under 200.. very rural location. anything i can do to make the reading better?
all rcd disconnection times are well within limits.
also I tested from the rod to the board for the main earthing conducter continuity its very low .02 ohms thats fine.
thanks in advance!
I have my niceic competent person scheme visit next week.
I have done the consumer unit change (I am pretty sure about the tests - just do them all)
Few Questions-
1. The second job I've done is adding a new circuit (just an outside light on its own breaker)
What tests would I be expected to carry out on this one?
as I am adding a new circuit I need to do a whole electrical installation cert. do i just write in the new circuit?
2. The first job is a TT system, what electrode test am I supposed to carry out. ? I have done the prospective earth fault current and got 280ohms, it says in the osg it should always be under 200.. very rural location. anything i can do to make the reading better?
all rcd disconnection times are well within limits.
also I tested from the rod to the board for the main earthing conducter continuity its very low .02 ohms thats fine.
thanks in advance!