Niceic cert filling in on software programme | Page 3 | on ElectriciansForums

Discuss Niceic cert filling in on software programme in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Joined
Dec 20, 2009
Messages
2,183
Reaction score
697
Location
Worcester
Wondering why they isn’t a Zs box to fill in,& if Connected to origin do not fill in box.
Also altered the Rcd times,now just entering the x5 trip time.
Why is there no N-E insulation reading ,& a L-L entry,which I would take to be L-N.
Just pondering these thoughts,will phone helpline next time in office,but any ideas.
 
I write the rccb in the circuit column if it’s a split load board, 61008, it’s current rating etc then I record only one rcd trip time measurement,I do not repeat the measurement to correspond to each circuit, for the column that covers 60898 devices I put N/A as it’s an mcb and not an rcbo.
 
I write the rccb in the circuit column if it’s a split load board, 61008, it’s current rating etc then I record only one rcd trip time measurement,I do not repeat the measurement to correspond to each circuit, for the column that covers 60898 devices I put N/A as it’s an mcb and not an rcbo.
I've seen this done before. Surely though we are recording the circuit details on each line, not just the device details. Every circuit under the RCD is protected by the RCD and therefore it is appropriate to enter the I delta n, and trip time on each of these circuits.
That's how I see it anyway.
 
I've seen this done before. Surely though we are recording the circuit details on each line, not just the device details. Every circuit under the RCD is protected by the RCD and therefore it is appropriate to enter the I delta n, and trip time on each of these circuits.
That's how I see it anyway.
I do record each circuit on each line but above I record the rccb, it’s rating, it’s I delta N etc then the circuits it protects underneath with its circuit number. One rcd, one trip time measurement, it’s just the way I do it, I used to do it that way before.
If they are rcbos then there’s an rcd trip time for each circuit corresponding to each line.
 
I do record each circuit on each line but above I record the rccb, it’s rating, it’s I delta N etc then the circuits it protects underneath with its circuit number. One rcd, one trip time measurement, it’s just the way I do it, I used to do it that way before.
If they are rcbos then there’s an rcd trip time for each circuit corresponding to each line.
So how do you show on the circuit schedule that the circuits following the RCD are in fact RCD protected?
Do you record the RCD as something like "RCD for circuits 5 to 10"?
 
So how do you show on the circuit schedule that the circuits following the RCD are in fact RCD protected?
Because I write the circuits underneath, then if there’s another rcd the other circuits are written under that one,
Just how I do it, by no means am I suggesting that it’s the be all and end all of doing it, as long as the information is recorded.
 

Attachments

  • [ElectriciansForums.net] Niceic cert filling in on software programme
    B82FA739-2836-469B-A67D-AA8EAA61C4A6.jpeg
    193.3 KB · Views: 31
For me that's not clear enough for someone else to interpret. Each to his own way I guess.
The other way it’s written to me suggests that the circuit have individual rcd protection as you have written 30mA for each 60898 and a trip time but there’s only one or two rcd’s etc.
so to me it’s written for rcbos when they’re are not any.
 
I have looked at three different Software program's for EICR reports, the best so far is "EasyCert" on a laptop or desktop, but not on a iPhone, the screen is too small, the software itself is quite intuitive and follows logical progress, but still has the annoying tick list page's, how much of that guff is really needed or even read by anyone that come's after? I suppose if you are that person that comes after and find a fault it may be useful, but then again you are going to do the whole tests yourself and not take a lot of notice of previous tests, or are you?
 
I don't believe that the ticks lists have any real merit and need a serious rethink. I'd be more in favour of a simple declaration that the works have been verified in accordance with the Standard and comply fully with it. This would not affect how the initial verification is carried out, but I think the paperwork is out of control.
 
I don't believe that the ticks lists have any real merit and need a serious rethink. I'd be more in favour of a simple declaration that the works have been verified in accordance with the Standard and comply fully with it. This would not affect how the initial verification is carried out, but I think the paperwork is out of control.
I think the whole of the legislation is out of control, can anyone answer "Why Part P"?
 
I write the rccb in the circuit column if it’s a split load board, 61008, it’s current rating etc then I record only one rcd trip time measurement,I do not repeat the measurement to correspond to each circuit, for the column that covers 60898 devices I put N/A as it’s an mcb and not an rcbo.
That’s pretty much what I said apart from the N/A if it’s 5 circuits on same rcd I repeat the 5 readings on 5 mcbs. If there are 5 rcbos then the 5 readings will be recorded independently
 
Because I write the circuits underneath, then if there’s another rcd the other circuits are written under that one,
Just how I do it, by no means am I suggesting that it’s the be all and end all of doing it, as long as the information is recorded.
Totally agree with you here. I was thinking how to record this and came up with the same idea.
 

Reply to Niceic cert filling in on software programme in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top