[FONT=Arial,Helvetica][SIZE=-1]Sorry just re read my post, didnt want to sound rude in my above post but wouldnt like to give out only enough information for you to fill in a few questions on a form without knowing you have enough information to correctly design & comission the detection.[/SIZE][/FONT][FONT=Arial,Helvetica][SIZE=-1]
[/SIZE][/FONT]
[FONT=Arial,Helvetica][SIZE=-1]
[/SIZE][/FONT]
[FONT=Arial,Helvetica][SIZE=-1]All sound level tests should be carried out with all doors closed.[/SIZE][/FONT]
[FONT=Arial,Helvetica][SIZE=-1]Hope this helps.[/SIZE][/FONT]
[FONT=Arial,Helvetica][SIZE=-1]Adam
[/SIZE][/FONT]
[FONT=Arial,Helvetica][SIZE=-1]
[/SIZE][/FONT]
[FONT=Arial,Helvetica][SIZE=-1]"The sound should not permanently damage hearing but it should be a minimum of 65dBA or 5dBA above any background noise likely to exceed 30 seconds. Should excessive noise be present, a visual indication of the alarm condition should also be provided. If the alarm is to wake sleeping occupants, such as in a hotel, the sound level should be a minimum of 75dBA at the bedhead. Sound level frequencies should normally be kept within the range of 500 to 1,000Hz[/SIZE][/FONT]
[FONT=Arial,Helvetica][SIZE=-1]
[/SIZE][/FONT]
[FONT=Arial,Helvetica][SIZE=-1]No matter how small the system, a minimum of two sounders are required and the correct sound levels must be maintained in all parts of the building.[/SIZE][/FONT]
[FONT=Arial,Helvetica][SIZE=-1]The sound level is reduced by approximately 20dBA by a door and by approximately 30dBA by a fire door.[/SIZE][/FONT]
[FONT=Arial,Helvetica][SIZE=-1]
[/SIZE][/FONT]
[FONT=Arial,Helvetica][SIZE=-1]Multiple small sounders produce a better sound distribution than a few large ones. In some areas, a large number of quieter sounders may be preferable to a few very loud sounders to prevent noise levels becoming too loud. Due to individual site characteristics, sound level checks should be carried out to ensure minimum sound levels are obtained."[/SIZE][/FONT]
I am assuming you are talking about mains powered smoke detectors? If you mean a 24v system with fire alarm control panel you need to comply to BS5839:1 not 6.
Adam