sorry to jump in guys so on a TN-C-S supply
on a SWA to a shed
at the db you wouldnt provide a 30 mA RCD to protect the SWA as its mechanically protected is it ok as he suggested to fix the SWA to fence does it need protecting with conduit or should it be buried in sand at a depth of 450mm ?? in Ducting and marked with tape
No need for RCD at supply end providing Zs of sub main is adequate.
SWA does not require protecting in conduit.
but deffo would provide one at the shed ccu for socket outlets
and would you not have to provide a Earth Electrode does it depend on the distance of the run
Yes RCD required at shed cu. No need for electrode unless main bonding is required to extraneous conductive parts.
is it ok to use 3 core armoured and use the 3rd core as the CPC
and do you still have to banjo the armouring of the swa at the Main DB/ccu
Yes & yes
sorry to jump in but i to am doing this at my brothers and using for my ELECSA assessment as well as changing the existing ccu and existing fuseboard in the house for 1 17th edition compliant ccu just so i know wether to get dual rcd split board or 3 way spit board with 2 rcds and couple of unprotected circuits sorry for all questions but just want to get it right
Hope that helps.