just got back from a customers ,hoping it a nice job and it was ,customers saying I cant push the isolator to the off position .
off comes the isolator wow that isolators fried ,so 6mm cable in and terminals tight has a ducks a88,now for the shower 9.5 kw .
now what about the rcd for it ,nice new bath room , wait a minute a 50amp so where is the rcd for this none .
looking at the 50amp no rcd, no rcbo and mem board and a wylex mcb . customer when was this fitted 3 months ago . so no test certs .
the customers says a bloke who comes to the local pub ,he does elcertics & plumbing came recommended and done a lot of bath rooms
so any test certs, why . if he does not test it then he is non compliant ,with who ,building control .so me and the customer had a chat about it .