I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring.

Some background first.
  1. It's an MK LN insulated [i.e. plastic] split load board, with only one side RCD protected. A direct predecessor [I think ?] and very similar in appearance to the plastic MK Sentry boards we know and love :-(
  2. At some stage, the customer has had an extension built, and the existing split-load board seems to have had the original MCBs on the unprotected side replaced with individual NIGLON RCBOs [presumably because they were cheaper at the time than the MK Sentry RCBOs which I think would have fitted]. The other side, with a mix of MK & NIGLON MCBs is protected by the OEM 80A RCCB.
  3. The 32A RCBO concerned was off, and popped off on trying to reset it. The customer said it would "used to stay on, but nowadays trips more or less constantly"
So:

I made sure all loads were disconnected. The RCBO still tripped, so not an appliance.

I disconnected conductors at the RCBO and tested the circuit:
  1. Ring conductors all continuous with similar readings [and expected values] for R1 & Rn, and the expected reading for R2.
  2. Insulation tests [@500V with all loads disconnected] ]showed >999 Megohms on P-N, P-E & N-E.
Figured it was the RCBO then. I reset it, and on the third attempt it stayed set. I then tested it with no loads connected. It tripped at 50% and wouldn't go any further.
I thought I'd just remove it and replace with an MK model. I'm fairly sure Sentry RCBOs fit these old LN type busbars with the right-angled fingers - seem to remember fitting a couple a few years back.

But I might be wrong?

Anyway... I released the busbar [after isolating the supply of course
[ElectriciansForums.net] Niglon RCBO stuck in MK LN board
] and the DIN rail locking catch on the RCBO. However, the RCBO stayed firmly where it was. I couldn't get it off the DIN rail.

I then had a closer look underneath, and it looks as if the original busbar is cut short, and extended with [perhaps?] a piece cannibalised from another type.

I think I have a complete old-type LN busbar somewhere, but what is worrying me is not being able easily to remove the RCBO.

I don't want to force it, break something and then have to do a board change for free. I wonder whether the person doing the mods possibly found the Niglon RCBOs "almost" fitted, but needed some persuasion and are now somehow jammed on the DIN rail?

[BTW don't get me started on the number of 32A circuits on a 60A Main Fuse -
[ElectriciansForums.net] Niglon RCBO stuck in MK LN board
]

Have I missed something blindingly obvious? I await scorn, brickbats etc...
[ElectriciansForums.net] Niglon RCBO stuck in MK LN board
[ElectriciansForums.net] Niglon RCBO stuck in MK LN board
[ElectriciansForums.net] Niglon RCBO stuck in MK LN board
[ElectriciansForums.net] Niglon RCBO stuck in MK LN board
 
Last edited by a moderator:
Remove the adjacent devices, slacken off ALL the bus terminals...... carefully placed whack with hammer.

After you've got it out, proceed to remove the rest of it and replace with a new board.
 

Reply to Niglon RCBO stuck in MK LN board in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
829

Similar threads

  • Question
The legs on the bus bar are too long for the new rcbos
Replies
3
Views
476
  • Question
What I find a little bit interesting is that there was an era of MFT's e.g. Robin, early Kewtech that tried to do non-trip loop tests using D-Lok...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top