Hi folks,

I've got a job where an RCD is tripping out on the upstairs lighting circuit where the cable runs in the loft are not accessible (unless of course I take the roof off or the ceilings down - neither of which are really feasible or customer friendly)!

I've checked all the fittings and can't see a problem. I've removed all lamps but still trips out. I'll do an Insulation test on it tomorrow - if this fails, will that prove the cable has been compromised somewhere in the loft?

Any ideas on easier fault finding?
 
You could disconnect the circuit completely, identify the switch cables, IR the switch cables if all OK then do a temp lash up with new cables on the loop from room to room and see if it all works as it should, if so then start reconnecting the old cables one by one to see where the fault is. Good luck, and lets us know the outcome.

Cheers......Howard
 
If the insulation test fails it only proves there is a fault somewhere on the whole circuit. if you are testing from the cu downstairs then the fault could be anywhere between there and the loft.
i don't want to state the obvious but before you make too many holes try to isolate the fault down to as small an area / length of cable as possible, break down at a fitting mid point test each way , then breakdown faulty section mid point/ @ a fitting again if possible and test each way etc etc.The cables may be accessible /jb'd under the floor upstairs?
good luck, hope its a quick one!!
 
Follow SDELEC's advice and you should be able to at least narrow it down, if not find it without any trouble.

You might like to look out for or try a few other things:
Pictures hanging nails above light switches
Pendant rose or fitting fixing screws that have peirced the cables above the ceiling
Do a low ohms (continuity) test L-E and L-N at various points along the circuit. If the fault is a direct short the lowest reading will be at the point closest to the fault.
The main supply cable from the consumer unit up to the loft is often out of zone as it passes behind the wall paster of the room above.
Use all you senses. Fault finding by smell is very underated!
There are other somewhat risky methods of finding such faults, I couldn't recommend them but they involve listening and looking for signs or arcing.
Good luck
 
Disconnect all the cables test each one seperately , that should identify the faulty leg , if its in the loft you might be lucky enough to pull a new one in by lashing to the old one . if not looks like a loft hatch/!
 
Thanks for your input guys. I'll check it out and let you know the outcome.

Thinking more about it now, "Bluetobits" comment regarding hanging hooks etc., slammed into walls may be the one, as they've hung an old five lamp WALL lantern by a big screw (time unknown) which is right above the wires coming out for the light fitting.

HOWEVER - these lights have been there for 15 years or so and the trip appeared to happen at 4am (known by the clock stopping on the cooker)!!

We'll see. I'll let you know......................
 
Well I found the fault chaps. Luckily the circuit cables had been run up to the light switches (don't know why?), and so testing each way was relatively easy. Found the faulty leg, lifted a couple of floor boards and found the fault in a cable running from a JB to a wall light which was wired into the circuit as it had a pull switch.

Job done.......
 

Reply to No access to loft Lighting Circuit tripping RCD in the Australia area at ElectriciansForums.net

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
341
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
570
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top