Done a consumer unit change on a property, all circuits tested ok only problem i've come to now is I can't see cooker isolator in kitchen?, looked behind units and back of draws, my guess is it has been plastered over. How now would I test this circuit without dissconecting from back ofthe big double oven/hob.. What are my options?
 
You havent got any, other than disconnect the oven.

Whilst you are at it, you may want to drop an isolator in and then connect the oven to that as per the norm.

It may be that when the kitchen was refitted, the isolator was done away with.
 
So there's no other option? What if the customer doesn't want to pay for me to pull kitchen units out trace the cable back and fit a new isolator?
 
test for insulation l+n to earth
test earth r2 meathod
and note it on cert


Quick thought.. Can Zs be calculated? Suppose I would need to know how much bigger the cpc is to live in 6mm (as in 1.67 x for 2.5mm T&E)..

Or can it just not be calculated?

So I won't be breaking any rules by not installing a cooker isolator aslong as I note it on cert?
 
Quick thought.. Can Zs be calculated? Suppose I would need to know how much bigger the cpc is to live in 6mm (as in 1.67 x for 2.5mm T&E)..

Or can it just not be calculated?

So I won't be breaking any rules by not installing a cooker isolator aslong as I note it on cert?

Zs = Ze +( R1+R2)

You can calculate R1+R2 from table 9A (App 9) of the On Site Guide if you know the length of the run.

This value will probs be a bit higher than the real value.
 
Reckon you are disconnecting the oven then ;)

Edit : or as beaver said if you have a long enough wandering lead you can work out R2 from the casing of the cooker and then calculate R1 as it will be the same length as the cpc
 
Last edited by a moderator:
If I were you I would test Zs and R1+R2 at oven terminals and make a note on cert that there's no isolator. Is it 6mm2 T+E at terminals, just thinking that there may be a join somewhere, but if visible cable is correct and tests ok, then that is all you can do. but tell the customer first, they might agree to fit one
 

Reply to No cooker isolator??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
686
  • Question
Have never used anything else. Room to dress 2 x 10mm2 T&E properly. Both flush metal boxes and surface boxes are available.
Replies
6
Views
689

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top