Not the usual per-1966 sort of "no CPC in wiring issue" but plastic light switches in plastic back-boxes in trunking wired in singles. The lights have CPCs and measured Zs, RCBO trip-time, etc, all good. However, the actual switches lack a CPC.

Now I could run in a CPC to meet the last paragraph of 411.3.1.1 but the problem is there is no terminal on either the back-box or the switch. Probably you can get back-box terminals as there is a bit that looks as if it was moulded for such a terminal, but as it stands absolutely nowhere to park the end.

So what do I do with the end of the cable? Leaving it in a Wago is the obvious thing to do, but I wondered if folks here have better advice?
 
I don’t think there’s too many options.
Are they normal switches? A few LAP switches wouldn’t cost a lot.
Otherwise yes I’d leave in a wago or in fact ideal connector (as they are cheaper and don’t have to make a good connection in this instance!)
 
Is this an observation on an EICR or are you undertaking other work on the circuit

If its just an EICR then you can make a note of your findings and thats that

If you are modifying / extending the lighting circuit then you might have to get some 1.5mm earth and attempt to get a bit to each switch just to cover your arse as you will have been the last person to alter the circuit
 
It is something I will be modifying at some point. The lack of CPC is really an issue for the letter of the regs as it would never be used, but of course we should apply the regs as best we can.
 

Reply to No CPC at light switches in plastic trunking in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
943

Similar threads

  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
978
  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
610

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top