steve447

I was asked to change a light fitting for a friend and replacing the old plastic pendant from a metal class I fitting but there is No cpc.
Without ripping out laminate flooring ect there is no no way i can get a cpc from the downstairs circuit, which this light is on.
The Upstairs circuit has cpc throughout the whole circuit and it would be a easy job to take a cpc from the upstairs circuit to this light.
Is this OK to do? I cant see anything in the regs that says no.

Cheers
 
Personally no I would not. For me it's keep the circuits separateas per the regs live-neutral and earth all back to the board as one circuit.
Reg 543.3.1 where a cpc consists of a separate cable it mustbe incorporated into the same wiring system as the live conductor

 
not a good idea, i would try and talk them out of it, i had same problem a few weeks ago and the customer wanted it doing no matter what so i wired the light to upstairs, not always possible due the way it wires but was ok for me.
 
Thanks guys, i have managed to find a way to get a earth down through the airing cupboard from the loft back to the CU.
Weird thing is that this light is the only one on the whole circuit with no cpc.
Must have been a partial rewire as it looks like some remedial work was done to sort out a shared neutral, why a cpc wasnt run with that i dont know.
 

Reply to No CPC on hall way lighting in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K
Yes I understand the setup now. Sorry about my confusing first post 🫢 It might be worth buying the Livolo switches you identified and lash at...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top