No CPC on lighting circuit | on ElectriciansForums
Discuss No CPC on lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
n180
No CPC at switches or light points.
All lights are class 2 so a C3 on eicr.
But what do I write for r1r2, just a LIM? is that acceptable?
bit confused on this.
It's not as simple as that, as I'm sure you're probably aware.
The Electrical Safety First Best Practice Guides have detailed information on this.
As for what to write in the R1+R2 column, it's not a limitation, because you have identified and mitigated the problem.
The only thing you can write is not applicable, as there is no CPC in the circuit.
Thanks loz.
Buzz, most are surface pattresses, 2 metal ones that will need to be changed out for surface pattresses.
Reply to No CPC on lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
My latest trick for this....if completely desperate and you have 3 very short cables .... Make a hole big enough for a quickwire to fit through...
It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.