Looking at a CU change for a young couple with kids.
There is no CPC on the lighting circuits, the cable is 2 core (red and black)
I have done a IR and continunity and all is ok, no borrowed neutrals
All the accessories are Class 2
The young couple don't have the budget to have the lighting circuits rewired.
I have got some no CPC warning lables for the CU and will state on the EIC that no CPC to lighting circuits, what readings do I put on the EIC for R1+R2 or R2?


Thanks
 
Slap a sticker on the consumer unit stating the lack of CPC on lighting circuit and that Class 1 fittings must not be used. Also ensure that back box lugs are of the insulated variety so that the 3.5mm box screws can not become live if a wire is damaged and pressed against the back box. There is also a recommendation in the ESC Best Practice Guide that a 30mA RCD should be fitted to provide additional protection. So long as you do all these things and note on any certificates that a CPC is not present then you have done as much as you can possibly do without carrying out a full rewire of the lighting circuit.
 
You could also use light switches which have plastic caps over the screws eg GET (ultimate if from TLC or wilts plus if from wilts).
 
If you can't obtain a reading that you should then it's defiantly a cross that goes in the box. so that would be a cross in ir n-e l-e. Also r1+r2, r2 and a cross in the zs box unless you state that you have carried out your zs via l-n on lighting circuits (which you will need to link out the rcd to obtain) and you will defiantly be needing to record comments on why the readings were not obtainable.Hope this helps.Carl
 

Reply to No CPC to lighting circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top