Had a discussion with a mate about this upcoming job, scenario is as follows -
TNCS to dwelling, 40a MCB @ DB1 (not RCD protected/not required) feeding 6mm2 3core SWA running through loft to outside wall (not buried in walls or ground anywhere) to DB2 (lean to timber shed attached to dwelling), DB2 - 100A DP Isolator with 2no. 30mA RCBO's, one supplying outside sockets in lean to, one supplying DB3 (outbuilding 20m from dwelling with extraneous conductive parts) supply to DB3 in 2core SWA buried @ 600mm in sand bed with warning tape to outbuilding, armour earthed at DB2 to TNCS, SWA armour insulated at DB3. 30ma DP RCD main switch at DB3, TT for DB3. So you have a 30ma RCBO protecting the 2 core SWA run, then a 30ma RCD at DB3. The issue being there is no discrimination between these two but does that matter as only DB3 supply will be affected, faults would trigger either the RBCO at DB2 or the RCD at DB3 but the same circuits will be affected (only those fed by DB3) Would a time delay 100ma RCD @ DB2 and an MCB be a better option......Thoughts please.....
 
Last edited by a moderator:
There is no requirement to rcd the swa to db3.! But there's nothing wrong with the two rcds just no discrimination.! If it gives you peace of mind and the customer is happy to pay for the extra protection carry on. What earth electrode was in place at db3 through curiosity?
 
It wouldn't cost that more then to upgrade to 10mm 3core, then you've got a decent earth also will be of adequate size for the bonding at the outbuilding and you wouldn't have to bother installing rods, etc.
 
Last edited:
Yeah true still more expensive than 2 core and rod hence original design. Splitting hairs but 6mm2 2core easier/quicker to work with than the 10mm2.....and extraneous conducive parts....
Don't want to open the exporting earth debate. Thanks for the comments, I've got the info I needed, will go through it with matey tomorrow.
 
Last edited by a moderator:
Because in the event of a neutral earth fault its a pain in the backside and how are you going to carry out the appropriate RCD tests when your tester will be set to 30ma? How will you know what RCD your readings are from when testing when both have tripped?

By connecting the "live" test probe to the outgoing "L", and the other to the incoming "N"? That's what I do when there's an upstream RCD as it doesn't cause an out of balance line / neutral current for the first RCD.
 

Reply to No discrimination, no problem??? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
794

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top