Been at a house today doing a pert rewire and new kitchen circuits. Noticed whilst under the floor boards that the smokes have been wired in 3 core flex, using the earth as the interconnect. Is this an acceptable way of doing things? Only reason I can think is that on the back of the detectors it states they are double insulated.:confused:
 
there is a couple of issues
there is a reg somewhere that says a green and yellow cable may not be overmarked and used as a live conductor
and the need to provide an earth in the cable and at the point
 
Even though its flex and the earth is insulated throughout, you MUST never use an earth for a phase/line ( not even if you sleeve it with phase/line).
Its in the regs as well (dont know what page though ).
Hope this helps,
Best regards,
Sav
 
But, can you sleeve the earth cable blue as neutral? i have seen it stated in this forum that it is ok to use 3 core flex to a bathroom fan
 
Hi Telectrix,
As animatter said, the neutral is a conductor and so you cannot use the earth for this.
also, as mentioned by Mr MarkSparks, we need to have an earth at the point.
 
agreed. i always use 3 core+earth. But when will the makers of bathroom fans make them to accept this?
 
When I contacted the NIC helpline and asked whether I could use 3 core flex, with cpc oversleeved as switched live, for an extractor fan (double insulated of coarse) I was told that they could see no reason why not as cpc same conductor size, also this would not require 1 core to be cut out(which they considered was a no no).
Also quote from NIC "you could do a complete rewire using flex if you wanted too".
Reg 514.4.2 states that SINGLE CORE cables that are coloured green/yellow throughout their length shall only be used as a protective conductor and shall not be overmarked.
 
Last edited by a moderator:
Didn't ask his name, just the question about using flex in fixed installations. If you don't agree with his answer please give reasons, reg numbers etc. I assume that NIC technical helpline is just that, a helpline, and not there to give duff information.
 
Strange as it may seem flex can be used for the fixed wiring of an installation. Last year we wired a large office block completely in flex apart from the sub mains. Although this installation was overseas it was all designed, installed and tested to BS 7671.
 
When I contacted the NIC helpline and asked whether I could use 3 core flex, with cpc oversleeved as switched live, for an extractor fan (double insulated of coarse) I was told that they could see no reason why not as cpc same conductor size, also this would not require 1 core to be cut out(which they considered was a no no).
Also quote from NIC "you could do a complete rewire using flex if you wanted too".
Reg 514.4.2 states that SINGLE CORE cables that are coloured green/yellow throughout their length shall only be used as a protective conductor and shall not be overmarked.

In this rare instance have to agree with the NICEIC man if it's not a single core cable and not a bare conductor within a sleeved cable then you can sleeve a yellow/green and use it as a live conductor. What you can't do is use the colour yellow/green as a live conductor.

521.9.1 also prooves him right about the flexible cable. Don't you just hate it when they are right
 

Reply to No earth to smoke detectors. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

This is it though…. To put one following the letter of the law, so to speak… would be a smoke in the hallway outside the bedroom door… then a heat...
    • Like
Replies
3
Views
313
  • Question
Personally I won't do fixed price work unless there is a clear spec for the job including things like smokes, data, TV whatever else the customer...
Replies
3
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top