Hello folks!
I tested a 300 year old cottage on Friday, wiring dates back to the 70s. It has 2 CU's, both 6 way wooden backed Wylex boards fitted with 3036 fuses.
The main switch feeding both CU's is the oldest 4293 RCD I have ever seen rated at 60A, tripping current is not marked but on a ramp test it tripped at 330mA.
There are a load of faults on the installation but the one that concerns me the most is there doesn't appear to be supply earth at all. Feeding the meter is a supply cable with only Line and Neutral, then whats looks like 25mm2 tails through the RCD to a henley block which then feeds the 2 CU's.
There is a bond at the water stopcock, 4mm2 max, and I am getting 0.08 ohms between that and the CU earth bar. No earth cables are labelled in the earth bar.
Ze at the CU's is 110.8 ohms!
What would you put on an inspection report regarding this?
I am thinking the only way forward is to recommend a new split load DB, new bonding to the water stopcock, possibly they will need an earth rod installing into the ground?
Talk about opening a can of worms! Like I say this is a 300 year old building, and its in a right state, full to the rafters with clutter.
What would you fellas put in your report about it?
I tested a 300 year old cottage on Friday, wiring dates back to the 70s. It has 2 CU's, both 6 way wooden backed Wylex boards fitted with 3036 fuses.
The main switch feeding both CU's is the oldest 4293 RCD I have ever seen rated at 60A, tripping current is not marked but on a ramp test it tripped at 330mA.
There are a load of faults on the installation but the one that concerns me the most is there doesn't appear to be supply earth at all. Feeding the meter is a supply cable with only Line and Neutral, then whats looks like 25mm2 tails through the RCD to a henley block which then feeds the 2 CU's.
There is a bond at the water stopcock, 4mm2 max, and I am getting 0.08 ohms between that and the CU earth bar. No earth cables are labelled in the earth bar.
Ze at the CU's is 110.8 ohms!
What would you put on an inspection report regarding this?
I am thinking the only way forward is to recommend a new split load DB, new bonding to the water stopcock, possibly they will need an earth rod installing into the ground?
Talk about opening a can of worms! Like I say this is a 300 year old building, and its in a right state, full to the rafters with clutter.
What would you fellas put in your report about it?