Just testing that the forum works OK.


Ive recently been appointed as the tester for a company which deals mainly with domestic properties. Having only ever tested my own installations on commercial / industrial installs, Ive never had any issues regarding the incoming supplies. However, when carrying out an EICR on a property I have failed to gain an acceptable reading for Ze or PEFC. I have the original test certs which confirm the prescence of an earth. I have informed the supplier who inform me that a team will be out to rectify the issue. This was last year and I am getting a little concerned that nothing has been done yet. Can anyone point me in the right direction as what I should do next ?

Cheers guys.
 
They would normally just fit an rcd to tide things over till they get around to sorting the problem
Is the installation Rcd protected ?
 
Ayup xbeazt. You don't say what sort of a supply it is or what you mean by no earth. How high is the Ze? There are a number of areas round here NWarwickshire+Leics with Ze considerably higher that the the normal 0.35 for TNCS and 0.8 for TNS and there is nothing you can do about it apart from complain to the supplier and fit an RCD. I do a lot of work on farms and out of the way locations on overhead lines. These are normally TT and it is normal to find Zes way up in the tens. At risk of telling you something you already know. Is it possible yours could be a TT? Sometimes its not immediately apparent where the supply comes in in SWA and looks like an incomer with an earth connection. I normally fit an Rcd and talk to the customer about getting the supplier in to make a TNCS connection on to the neutral.
Howard
 
I wouldnt use a previous test certificate to find out the type of earthing system used. If it is a PME or TN-S supply and the Ze is above the set limits then contact the DNO who have a responsibility to maintain the earth connection. They should attend within a specifed te limit too if it is too high for the type of esrth connection.

If it is a TT then you will need to fit the relevant RCDs as stated above and also ensure the Ra value is satisfactory.
 
The installation is a TNS system. The previous test sheets show an acceptable reading of 0.38 ohms for Ze and my reading is 283 ohms. The earth strap connected to the incomer has clearly been on for some time. The board is a 16th edition split load with just the ring mains on two breakers and Ive just installed a separate board for a new kitchen extention but cant complete the certs until I get a main earth.

Does anyone know the reason for having no earth. Its obviously at the transformer end.
 
How long ago was the last inspection done, can't see it jumping so high unless the problem was there the last inspection and they couldn't be bothered to investigate. I would double check it definitely isn't tt. From that reading that's what I would be looking for. If not contact dno and let them know what you have tested and the reading you have
 
If it is a TN-S you need to contact the DNO asap as they have a resonsibilty to maintain it and should act as a emergency call out. No need to worty futher once they have been contacted as it then becomes there liability but it wolud be worth advising the customer to turn off there DB until it has been repaired to a saisfactory state.
 
I can clearly see the earth strap on the outer sheath of the main incomer which comes from the ground up. All the surrounding properties are of the same design. On Monday I will make my 4th phone call to the supplier, they also confirmed the supply type on my initial phone call and are aware that there is an immediate issue. I was also under the assumption that it was treated as an emergency and would be sorted pretty swiftly. The main issue is that this property is used as a care home for mentally ill people. But the suppliers dont seem to care at all.
 
The installation is a TNS system. The previous test sheets show an acceptable reading of 0.38 ohms for Ze and my reading is 283 ohms. The earth strap connected to the incomer has clearly been on for some time. The board is a 16th edition split load with just the ring mains on two breakers and Ive just installed a separate board for a new kitchen extention but cant complete the certs until I get a main earth.

Does anyone know the reason for having no earth. Its obviously at the transformer end.



One or other of these statements needs explaining
If there is a high resistance earth,the chances are they have repaired or renewed a cable somewhere along the line,as stated previously,their action would be to fit an rcd as a temporary measure,it may be that the supply has been converted to Pme and that facility is available

Whether its them or you.an rcd needs to cover those unprotected circuits. Couldn't you shift the mcbs over for now or fit a rcd instead of the main switch

It seems to be an issue for them to solve, but at the same time,it is yours or your customers responsibility to make the installation safe,even if only temporary
 

Reply to no earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
385
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

That is what i am going to do. Thanks mate!
Replies
11
Views
692
So it's OK to use a backbox with isolated lugs - even though the switch and the wiring in the box won't meet the standards for Class II. Plus the...
Replies
7
Views
466

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top