no main bond | on ElectriciansForums
Discuss no main bond in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
the pict
Mentor
Brodick
My house, no main bond as there is nothing to bond to, water services and central heating in plastic, no gas, no steel work, so on the cert is it a N/A
Pict
Pict
Hold on a sec, your right lads if it's not 'Extraneous' we don't bond it I would still take a measurement between MET and the services where and if they turn from plastic to copper the Gas deffo will, water possibly, we know why we dont randomly bond metal,by testing the reading between MET and the copper we are making sure, there could be some central heating pipes passing through an earth potential we just don't know ?
J
Reply to no main bond in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
loz2754
L
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...