Evening..
I have just completed an EICR. The incoming gas pipe has been hidden behind kitchen units. I have dismantled the plinths, emptied the cupboards and used my inspection camera all to no avail. I cannot see any main bonding.
I can just get my hand through an inspection hole cut in the back of one unit and reach the incoming gas to get a crocodile clip on to it. I get a reading of 0.05Ω using a wander lead back to the MET.
In the CU there is a 10mm bonding cable which I have identified for the water, then there are 2 unidentified 6mm earthing/bonding conductors.
I have to admit I'm at a bit of a loss as to which code to give this? No main bonding is a C2, but with a reading of 0.05Ω!!?? The CU is approx 8m away from incoming gas pipe.
Any suggestions? Running a new 10mm would mean taking up laminate and kitchen floor tiles or making lots of holes in the ceiling which seems a bit crazy given such a low continuity reading which leads me to think it is bonded somewhere behind the units.
I have just completed an EICR. The incoming gas pipe has been hidden behind kitchen units. I have dismantled the plinths, emptied the cupboards and used my inspection camera all to no avail. I cannot see any main bonding.
I can just get my hand through an inspection hole cut in the back of one unit and reach the incoming gas to get a crocodile clip on to it. I get a reading of 0.05Ω using a wander lead back to the MET.
In the CU there is a 10mm bonding cable which I have identified for the water, then there are 2 unidentified 6mm earthing/bonding conductors.
I have to admit I'm at a bit of a loss as to which code to give this? No main bonding is a C2, but with a reading of 0.05Ω!!?? The CU is approx 8m away from incoming gas pipe.
Any suggestions? Running a new 10mm would mean taking up laminate and kitchen floor tiles or making lots of holes in the ceiling which seems a bit crazy given such a low continuity reading which leads me to think it is bonded somewhere behind the units.