B

Benny_Boy

Evening all, bit late I know but...

Just been to a house today and the owner (rental) wants me to do the remedial work thrown up by a PIR made by a different company.

There are a few areas that need attention but one of the items on the list was no main bonding to water.
There is 10mm main bonding to the gas pipe but that's the only bonding conductor in the MET.
On further investigation it seems that the water incomer is "supplementarily" bonded with 10mm to a gas pipe and the resistance from the incoming water supply pipe to the gas main bonding conductor where it meets the MET is 0.03 Ohms.

Do I still need to run separate bonding for the water even though we're well under?
I'm presuming yes but I think in 16th ed (when this was installed) there was no requirement to have separate bonding conductors for each service. In essence, do you have to bring an older installation up to the most recent regs every time even though it's safe?

any opinions/suggestions appreciated
 
Evening all, bit late I know but...

Just been to a house today and the owner (rental) wants me to do the remedial work thrown up by a PIR made by a different company.

There are a few areas that need attention but one of the items on the list was no main bonding to water.
There is 10mm main bonding to the gas pipe but that's the only bonding conductor in the MET.
On further investigation it seems that the water incomer is "supplementarily" bonded with 10mm to a gas pipe and the resistance from the incoming water supply pipe to the gas main bonding conductor where it meets the MET is 0.03 Ohms.

Do I still need to run separate bonding for the water even though we're well under?
I'm presuming yes but I think in 16th ed (when this was installed) there was no requirement to have separate bonding conductors for each service. In essence, do you have to bring an older installation up to the most recent regs every time even though it's safe?

any opinions/suggestions appreciated


i might be wrong but you need a seperate 10mm to water unless it is a continuous are welded joint, because if the gas was stripped out for any reason you would loose the water bond
 
yeah, that's kind of what I thought.

I just remember my old lecturer saying that just because something doesn't comply now as a result of a regs change, it doesn't mean that it's unsafe.

I suppose what I'm really asking is, what code number would you give this non compliance?
 
Code 1.

Could you not make a crimped or soldered connection onto your gas bond and keep it continious to the water.

Correct me if i am wrong but this still would not have complied with the 16th.
 
Last edited:
Code 1.

Could you not make a crimped or soldered connection onto your gas bond and keep it continious to the water.

Correct me if i am wrong but this still would not have complied with the 16th.

The water is only bonded to the gas pipe. it's also a good way away from the MET, several rooms and floorboards to get through to get back. I was quite surprised to get such a low reading from the water pipe to the MET.

I see what you're saying about the gas bond but what I didn't mention is that the gas incomer is only just <150mm away from the CU!

Looks like I have some bad news for the owner!
 
Sorry didn't read 1st post properly i took it that 10mm to water was beside or close to main bond to gas.
not your fault mate!

I didn't say that the gas was next to the CU and that the water was miles away
 
Last edited by a moderator:

Reply to no main bonding to water in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
609
loz2754
L

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top