I am pricing to wire a kitchen and intend to feed it with one ring circuit.
The client is looking for 5 x twin skts. above worktop level, and as many as 6 x dedicated appliance sockets which he would like switched through a grid system above worktop level.
Chapter 7.2.2 (para 3) in the OSG states that " ... the number of non-fused spurs is not to exceed the total number of socket outlets and items of stationary equipment connected directly in the circuit."
I intended installing one - perhaps two - grids in the ring circuit, looping in and out of the supply side of 20amp switches (to maintain the ring) and then spurring off in 2.5mm to either an fcu or unswitched socket for connection to the appliance.
Am I able to do this, or should I install more sockets on the ring to make up the numbers - it does seem a bit odd to have to do that.
Any advice would be appreciated; I haven't used this system of labelled 20a grid switches before, normally I just include an fcu in the ring above the worktop and drop down to the connection unit/socket, but the customer is looking for a tidy job.
The client is looking for 5 x twin skts. above worktop level, and as many as 6 x dedicated appliance sockets which he would like switched through a grid system above worktop level.
Chapter 7.2.2 (para 3) in the OSG states that " ... the number of non-fused spurs is not to exceed the total number of socket outlets and items of stationary equipment connected directly in the circuit."
I intended installing one - perhaps two - grids in the ring circuit, looping in and out of the supply side of 20amp switches (to maintain the ring) and then spurring off in 2.5mm to either an fcu or unswitched socket for connection to the appliance.
Am I able to do this, or should I install more sockets on the ring to make up the numbers - it does seem a bit odd to have to do that.
Any advice would be appreciated; I haven't used this system of labelled 20a grid switches before, normally I just include an fcu in the ring above the worktop and drop down to the connection unit/socket, but the customer is looking for a tidy job.