Can anyone help me with this

I have a old plastic consumer unit with one rcd with lighting and cooker not on rcd
The original lighting circuit has been altered over the years and 16 non fire rated spotlights put in the kitchen with all earths cut out
2 bathrooms 5 spotlights in each not iP rated and earths cut out again
Would this fail an eicr due to no rcd on cooker circuit and lights with the original wiring being altered and not been put on rcd when the spotlights was done and now cause they have to be replaced anyway this would now require an rcd
 
You cannot fail an eicr, but you will receive at unsatisfactory report due to the lack of earth at each point. If the circuit is altered in any way then it will be the responsibility of the electrician to ensure it is compliant, likely meaning it will need rcd protection.
 
The circuits not on rcd would be a c3, improvement,
but as above, not having earths at each light point C2. Potentially dangerous
Assuming they are mains spotlights.
if they are selv then they don’t need an earth taking to each point.
 
So would you say even tho the spotlights that was a addition to the original wiring they don’t require rcd even if replacing them all and rectifying the earth problem

Same with the cooker it’s clearly an addition after the original wiring so shouldn’t it of been put on rcd when installed and shouldn’t it be put on rcd anyway now
 
If they are being replaced the earths will require being connected. That's an alteration to a circuit and therefore will require rcd protection to be complaint.
 

Reply to No rcd on lights and cooker in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
382
  • Question
none at all.... and the rcd trips within specification... test button operational.... nothing to suggest there's a problem until you take the...
    • Like
Replies
2
Views
613

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top