I’m doing some tests on my board at home in order to prepare it for an upgrade. It’s an old plastic GE board with no rcd protection. Doing continuity of ring final circuit on the main ring. When it comes to end to end tests at the consumer unit I’m getting no reading between neutrals. All good between L-L and E-E. Figure of eight and I’m testing L-N on sockets and all readings come good (0.45-0.50 ohms) in every room. What could be the cause of this? ? Neutrals terminated badly at a socket somewhere? Rodents? JB?

Would taking one leg of ring out and looking with a Martin dale be a quick solution to find it before I start looking by splitting the ring?

Insulation resistance was L-N >299Mohms, L-E >299Mohms but N-E only 8Mohms.
 
Does get me worried about , IR tests for rest of installation !


Was more thinking ,of a reluctance to have an " RCD" type Master switch.
( any defects getting ignored - Must admit I am guilty of skimming thread...
my brain solving other issues at moment )
as I took RCCB on just 1 circuit ! (and not IR test- risks to RCCB)
 
Why didn't you just replace the main switch with the rcd instead of doctoring one in.
i'd think he did it that way or he would have had to work live or diss, tail/s from meter. ( assuming no up front isolator. ).
 
You don't have any selectivity now between rcd and downstream mcb's, an earth fault will likely trip your rcd which means you will loose whole installation. IMHO better option would be to install individual rcbo's
think OP has done it temporary till he can get round to replacing CU.
 
think OP has done it temporary till he can get round to replacing CU.

Exactly, yes. And I agree ? will be swapping it for a new CU eventually.

All points regarding rcd as a main switch taken on board, every day is a learning day ?‍♂️

Ps as I said earlier, isolating the board by pulling the main fuse doesn’t make it 100% safe because neutral shares same enclosure with my neighbours installation. Please tell me if I’m wrong? I posted some pictures earlier in the thread for you to see what I’m on about ?
The only way to look inside is to pull my neighbours fuse because it blocks the lid where neutrals are terminated and I want to avoid doing that.
 
You've posted a pic. of your CU with two grey tails going into it, and you've posted a pic of your service head with a blue, red, and brown tail leading from it. Could you post a pic of where these tails meet, please.
Should be a meter somewhere.
 
On a TNC-S theoretically the neutral and earth should be at the same potential as they're linked at the supply head.

On a TN-S theoretically the earth and neutral could be at the same potential as they're linked at the transformer but there may be resistance differences on the cables and sheath causing a potential difference.

On a TT neutral and earth potentials could be significantly different.

TBH with a shared supply I'd take the much safer option of dropping the tails out of the consumer side of the meter, technically these belong to the consumer so they have the legal right to do this although breaking the seals on the meter could be classed as criminal damage as they belong to the supplier... ??

If possible I would add a main isolator switch to avoid this in the future and make additions/alterations much easier and safer.

As for having an RCD main switch I try to avoid them as one fault will effect the whole installation.
 
You've posted a pic. of your CU with two grey tails going into it, and you've posted a pic of your service head with a blue, red, and brown tail leading from it. Could you post a pic of where these tails meet, please.
Should be a meter somewhere.
[ElectriciansForums.net] No reading N-N end to end on a ring main


Here’s a pic of the whole thing. TNS system. Quite tight for space if I added an isolator before the CU. I had to pull up my cables from the board as I had no space inside and kept the slack for future when I upgrade it. I will be using some fire rated glands. Ps, yes, my neighbours have their rcd as a mains switch I know ?
 

Reply to No reading N-N end to end on a ring main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
349
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top