I’m doing some tests on my board at home in order to prepare it for an upgrade. It’s an old plastic GE board with no rcd protection. Doing continuity of ring final circuit on the main ring. When it comes to end to end tests at the consumer unit I’m getting no reading between neutrals. All good between L-L and E-E. Figure of eight and I’m testing L-N on sockets and all readings come good (0.45-0.50 ohms) in every room. What could be the cause of this? ? Neutrals terminated badly at a socket somewhere? Rodents? JB?
Would taking one leg of ring out and looking with a Martin dale be a quick solution to find it before I start looking by splitting the ring?
Insulation resistance was L-N >299Mohms, L-E >299Mohms but N-E only 8Mohms.
Would taking one leg of ring out and looking with a Martin dale be a quick solution to find it before I start looking by splitting the ring?
Insulation resistance was L-N >299Mohms, L-E >299Mohms but N-E only 8Mohms.