No reading N-N end to end on a ring main | on ElectriciansForums

Discuss No reading N-N end to end on a ring main in the UK Electrical Forum area at ElectriciansForums.net

Kuba

-
Joined
May 14, 2019
Messages
57
Reaction score
46
Location
London
I’m doing some tests on my board at home in order to prepare it for an upgrade. It’s an old plastic GE board with no rcd protection. Doing continuity of ring final circuit on the main ring. When it comes to end to end tests at the consumer unit I’m getting no reading between neutrals. All good between L-L and E-E. Figure of eight and I’m testing L-N on sockets and all readings come good (0.45-0.50 ohms) in every room. What could be the cause of this? ? Neutrals terminated badly at a socket somewhere? Rodents? JB?

Would taking one leg of ring out and looking with a Martin dale be a quick solution to find it before I start looking by splitting the ring?

Insulation resistance was L-N >299Mohms, L-E >299Mohms but N-E only 8Mohms.
 
No point doing the cross-connections (figure of 8) if you don't have rn continuity. That needs sorted first. Probably loose connection on the neutral in a socket-outlet or screwed onto insulation. So it might be worth checking all connections including the phase and cpc.

I presume you've checked that the neutrals aren't mixed up in the DB?
 
most likely is that a N has come out of a socket terminal. any case that's the easiest check to do, just by inspecting each outlet. if not, then short 1 end L-N at CU, go round sockets mesuring L-N resistance. this will track the fault location. or you could do N-E.
 
No point doing the cross-connections (figure of 8) if you don't have rn continuity. That needs sorted first. Probably loose connection on the neutral in a socket-outlet or screwed onto insulation. So it might be worth checking all connections including the phase and cpc.

I presume you've checked that the neutrals aren't mixed up in the DB?

Yes I have tidied up and dressed all cables so I’ve got a pretty clear view of what’s what.

Someone told me that disconnecting one leg and checking each socket with a Martin dale socket tester is an easy and quick search. Should I give this a go? Otherwise I’ll follow what @telectrix suggested ?
 
You suggest disconnecting one end of the ring, leaving the other powered, and going round with a Martindale to find the which are live L-N and which are dead. Yes, that will work, however it is a live test and where possible, dead tests with a resistance meter are often safer and possibly easier. If you short N-E at one end in the board and go round testing for continuity, you can open any suspect points immediately to check, without having to isolate, inspect, close up, re-energise and start testing again. The break could be at the last socket with continuity, the first one without, or somewhere between, so it could be a nuisance having to re-energise each time to use the Martindale.
 
You suggest disconnecting one end of the ring, leaving the other powered, and going round with a Martindale to find the which are live L-N and which are dead. Yes, that will work, however it is a live test and where possible, dead tests with a resistance meter are often safer and possibly easier. If you short N-E at one end in the board and go round testing for continuity, you can open any suspect points immediately to check, without having to isolate, inspect, close up, re-energise and start testing again. The break could be at the last socket with continuity, the first one without, or somewhere between, so it could be a nuisance having to re-energise each time to use the Martindale.

Thank you @Lucien Nunes for the advice ? I found it quite fast too.

[ElectriciansForums.net] No reading N-N end to end on a ring main

[ElectriciansForums.net] No reading N-N end to end on a ring main
 
It may be good idea to switch off main switch next time, especially when you have nice shiny live busbar exposed like that
where's the fun in that?
 

Reply to No reading N-N end to end on a ring main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
349
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top