Good morning... been called out to replace a DB on this domestic supply... no earth noticed and only bonding is 6mm from the incoming water supply...















Any advice as to how to document this would be greatly appreciated.. would like to get certification correct without any guess work...















Was a late call out to view the current setup so haven't done any Ze or pfc testing as yet...








[ElectriciansForums.net] No sign of Earthing...?







Thanks in advance...













 

Attachments

  • [ElectriciansForums.net] No sign of Earthing...?
    Screenshot_20230307_103434_Gallery.jpg
    384 KB · Views: 67
It looks old and I have seen that before when it was using the water pipe as a means of earthing, something that has not been permitted for a few editions and many decades of the wiring regs! Historically that would often get a low enough Ze to allow OCPD-based disconnection on most fuses but obviously is no longer permitted for various reasons, the use of plastic water pipe being the most obvious one that would render ADS impossible.

If the DNO can't/won't provide a supply earth it would need to be made TT with a rod and suitable means of achieving ADS (realistically, RCDs all round).
 
You can’t proceed without either
a) speaking to DNO and seeing what their records say, and trying to get the DNO to provide an earth (which will likely cost unless you are lucky)
b) creating your own TT earthing
 
There are loads of old places around me where the sole means of earthing is via a single bond to the incoming water pipe

Sometimes I have managed to get the DNO to make it a PME , and sometimes I get no joy with the DNO and have no choice but to TT it

One old massive house I went to change some electric heaters that had a Zs at a socket 250 some odd ohms , so I investigated further to find the entire house was relying on a 1.5mm green wrapped around the water pipe
 
It looks old

Old but not truly ancient. Note the white phase marker disc pinned to the meter board to the left of the service cable.
 

Reply to No sign of Earthing...? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
711

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top