No ze at origin of tt system | on ElectriciansForums
Discuss No ze at origin of tt system in the The Welcome Forum area at ElectriciansForums.net
Helston
Hi guys, cannot get a resistance reading when using my Robin loop tester. It just shows 204v and the red do not proceed lamp lit.
Never come across this before any ideas would be appreciated. (The live neutral reading is 243v)
New rod fitted and driven in to good ground at about 2.3 meters.
Where is the installation? Can you see the supply transformer? Is the rod in good ground ie not made up/ back fill. Out of interest is the old rod still in place could you test that for reference. Have you in stalled a new earth conductor or reusing existing? If you are testing remote of the rod then what earth continuity reading did you get ?
Hi - only basic thoughts, sorry - confirm rod actually connected to met (wander lead). Confirm tester (test at another site, check batteries). My KT65 measured a TT earth loop over 300 Ohms last week, it was corrosion at the rod to cable connection, thankfully :) .
Could be like mine was today o_O
I can see the supply tranny and the rod is new and gone in very good ground. The old rod was giving the same problem so cant use that as a reference. Just never had this before. My only thing i can perhaps think of is volts drop but line to neutral reading comes up as 243v so no problem there.
If you are attempting to measure the resistance of the electrode that connects to a generator you need an earth electrode tester as the rod will be referencing the generator neutral to earth.
Attempting to use an earth fault loop impedance tester will not work as the electrode doesn’t form part of the earth fault loop impedance path.
Either that or I have misunderstood your post.
As in #7 have you done a continuity test of the earthing conductor to the electrode.
What Robin tester is it.
That tester will measure up to 2000 ohm and it is unusual to get a do not proceed indicator unless polarity is incorrect or you have an almost non existent earth, I use one day in day out.
Reply to No ze at origin of tt system in the The Welcome Forum area at ElectriciansForums.net