leestaf

Hi all
I have tested a small house and have continuity of ring conductors at the CU, I have tried to gain a measurement at the kitchen sockets for Zs but my meter says >200 suggesting open circuit however if i plug my Martindale in it says all is ok and no dropped earths?????? There is only one ring maion for the small power in the house as its a tiny 2 up 2 down. Any Help/Ideas guys???
Thanks in advance
 
>200 doesn't necessary mean open circuit, it could be that the Zs is beyond the range of the instrument. Have you obtained a value of Ze?

Does your martindale given values of EFLI or just indicate polarity?
 
Last edited:
Tester tried before and after on other points and all fine, meters came back from calibration week before, plug in tester tried the same way and working fine. Cant understand why PIT is sensitive enough to pick up earth but meters arent? or could it be im barking??
 
are yo saying that the >200 is just on the kitchen sockets? if so, sounds like a polarity reversal somewhere.
 
Hi Lee, What are your continuity readings for the ring? I presume the ring is RCD additionally protected and you are attempting to perform a no-trip loop test? Others have reported sometimes the RCD introducing an apparent additional impedance when testing in no-trip with some testers. To check this disconnect the final circuits from the RCD and no-trip loop test directly at RCD output terminals, if the reading is significantly different to your recorded Ze you have confirmed an apparent RCD impedance cause by the particular test method and/or instrument used. If this is the case reconnect the final circuits and record the calculated Zs from Zs=Ze +(R1+R2).
 
Hi Guys
Thanks for help so far
The continuity readings are fine 0.7 0.7 and 1.25, the polarity is ok and this woulld have been picked up by the tester as it wont perform if polarity is wrong. Ins Res is 11.24 on L-E but wouldnt think this would result in >200 measurement.
Junction box could be a possibillity but i hope not as the kitchen has a flat roof and no access so unless YeeeHaaa Joe has been at work i would'nt expect JB's
BS3036 fuseboard at present so no RCD but im due to upgrade to 17th CU as part of remedials of a dom PIR.
Think a little further investigation required to fix this.
Many Thanks to you all
 
Lee how many sockets are not allowing you to test for the Zs? Was wondering if for some abstract reason the BS 1363 leads was not making contacts in the socket properly?

Are any other sockets in the house giving you the same problem. If not then I think the best way to do this is with a wander lead one end attached to one end of the ring cable at the CU and with a socket adapter go around testing continuity at each socket just to make sure everything is as it should
 
Good idea Malcolm will do,there are 4 x 2g sockets in the small galley kitchen however as the house is a 2 up 2 down the kitchen is extended to the rear of the property and this'd It's where the problem is. I doubt its a coincidence bit will give the ****** lead a go cheers.
 

Reply to No zs???? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
855

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top