I've just had a really interesting chat about this that's led on to all sorts of other relevant topics.
Suffice to say, that there definitely isn't a 200W/m2 limit specified anywhere, and Elecsa think this probably got a bit lost in translation somewhere, although it's true that the instruments and calculations will all be more accurate at those sort of levels.
They did point to BS62446 guidance for inspection and testing of solar PV systems, which apparently contains a reference to the measurement of the irradiance levels being taken at the same time as the DC test readings, and being to within a 5% tolerance. If we all worked to that though, unless you've got one of the all in one test units, it'd make it virtually impossible to actually test the circuits from the internal DC isolator - unless you've got a second person taking the light levels at the exact same time.
Also as the accuracy of the light meters is relatively low at low light levels, and no record is kept of the actual temperature of the cells, it's just not possible to calculate the figures backwards as accurately as they've tried to do here... a point that was taken on board and both agreed with and disagreed with, so I'm not sure what the final outcome was there, other than that rigid adherence to guidance that assumes accuracy where no accuracy should ever be assumed isn't particularly sensible, and that the point of the tests is mainly to check if the figures are in the right ball park for the correct number of panels being connected, and ideally all the strings within the panels being operational.... though I personally can't see how this can be done without any reference to panel temperature.
Suffice to say, that there definitely isn't a 200W/m2 limit specified anywhere, and Elecsa think this probably got a bit lost in translation somewhere, although it's true that the instruments and calculations will all be more accurate at those sort of levels.
They did point to BS62446 guidance for inspection and testing of solar PV systems, which apparently contains a reference to the measurement of the irradiance levels being taken at the same time as the DC test readings, and being to within a 5% tolerance. If we all worked to that though, unless you've got one of the all in one test units, it'd make it virtually impossible to actually test the circuits from the internal DC isolator - unless you've got a second person taking the light levels at the exact same time.
Also as the accuracy of the light meters is relatively low at low light levels, and no record is kept of the actual temperature of the cells, it's just not possible to calculate the figures backwards as accurately as they've tried to do here... a point that was taken on board and both agreed with and disagreed with, so I'm not sure what the final outcome was there, other than that rigid adherence to guidance that assumes accuracy where no accuracy should ever be assumed isn't particularly sensible, and that the point of the tests is mainly to check if the figures are in the right ball park for the correct number of panels being connected, and ideally all the strings within the panels being operational.... though I personally can't see how this can be done without any reference to panel temperature.