J

jools p

I have a megger 1552 and the no trip setting works fine, until today. Can't get a loop reading on a sub main in workshop. It keeps tripping the RCD back in the house. Some RCD's I have found to be ultra sensitive but not this one. Cutting cables all day on switched off circuits and never a trip but go and do the test and pop off it goes. Whats that all about..
 
Exactly as you said, some RCD;s are more sensitive then others.

I have just fitted a new GE budget CU today and none of it tripped once.

I have had crabtree and hager which sometimes trip and sometimes dont.

Make sure your probes are pushed in tight before and during the test. Sometimes if one is loose that will also cause them to let go.
 
I have a megger 1552 and the no trip setting works fine, until today. Can't get a loop reading on a sub main in workshop. It keeps tripping the RCD back in the house. Some RCD's I have found to be ultra sensitive but not this one. Cutting cables all day on switched off circuits and never a trip but go and do the test and pop off it goes. Whats that all about..

I take it you have RCD discrimination between house board and sub board?

Can't see how this would make a difference but it would be interesting to try the test in the sub board with the RCD in the house board isolated?

I have a Megger MFT 1552 silly question but your not using HI-Loop?
 
check your tester on a system you know to be ok. your house. that will tell you your testers ok.
Did you do a rcd nuisence trip test? see if the rcd's ok
 

Reply to non trip loop test still trips the rcd in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
673
davesparks
D
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top