Not enough power | on ElectriciansForums
Discuss Not enough power in the Australia area at ElectriciansForums.net
N
nrg
Hi
I have a customer with a large house, workshop and pool. He is wanting to add a heat exchanger to his pool house and get rid of his oil boiler.
He has the following setup
40amp RCBO from main board - 6mm T/E to Dis Board 1
Dis Board 1 has 32amp (4mm) to Dis Board 2 (pool house)
Dis Board 2 has 16amp, 16amp, 6amp, 6amp
The issue is he has been told by his supplier of the heat exchanger that he needs to have an over current protection breaker of 40amps Type C (Hi start up current)
Can anyone give me any advice on how to get the customer what he needs? thanks
eco7 Models
Model Electrical Power Heat Output
Kw (at 24c) Heat Output
Kw (at 15c) COP
RRP (not our prices !)
VA-WPH10
Single Phase 50hz 9.5kw 8.7k. 4.8-4.6 £1610
VA-WPH20 Single phase 50hz 12.5kw 9.5kw 6.5-6.2 £2080
VA-WPH40 Single phase 50hz 17.4kw 16.0kw 6.3-6.1 £3200
VA-WPH60L Single phase 50hz 27kw 25kw 5.2-5.0 £4150
VA-WPH60 3-Phase 50hz 27kw 25kw 5.2-4.55 £4150
You're probably going to need a larger supply directly to the poolhouse from the Main board. What are the distances involved. Do you know the exact start and run current figures of the heat pump?
Edit. The heat pump would be sized according to the size and type of pool. Do you know which model has been specified?
I was going to but a 50 RCBO on the main board and upgrade the cable to 10mm and then upgrade the 32 to a 45mcb and run 10/6mm to the pool house.
The running power is 27 amps and can spike on startup to 50+ amp!
I know but as with most domestic properties it's only single phase! I'm a bit stumped as to the best way forward. Thanks for the help thus far, if you have any other suggestions I'd be glad to here them.
Reply to Not enough power in the Australia area at ElectriciansForums.net
Question 1 do you prefer buttered, salted or sweet salted? I'm guessing salty 😜 1. Auto range multimeter (used on mains before when testing the...
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...