Hi everyone...
I was hoping for some advice on a circuit to a summerhouse that was part of a p.i.r. i have been doing today,
There was a garage type unit with the usual two ways for sockets and lighting, metal clad, and the sub main is 6mm s.w.a., this end is on a TT rodded down well with a reading of 31 ohms, the s.w.a is under ground and makes its way back to the main consumer unit and into a connection box on the outside of the house where the armour is terminated, conductors then pass through the walls in 20 mm conduit from the back of the external connection box into a cooker control switch so that the homeowner can isolate the summer house from inside the house.. s.w.a connect into secondary side of cooker switch and c.p.c terminates into earth terminal as norm...now ...the switch is next to the c.u., and running from an 32 amp breaker, are line and neutral, but no c.p.c, to the primary side of the cooker switch,ther are no r.c.ds on main c.u.... is there anything i should be noting here??( regarding the sub main that is)

Thanks in advance,,
Jemma
 
Last edited by a moderator:
So, if I'm reading it correctly, a L-E short circuit on the SWA sub-main wouldn't cause any upstream device to operate as there is no earth fault path back to the main CU in the house???

If for example someone were to damage the SWA with a spade bewteen L-E, no device would operate to shut off the supply at the house as there isn't a cpc connected to the armouring.
 
Only things I can think of:
Is the garage CU in the summer house 30mA RCD protected as you have sockets there and on a TT.
Is the CPC from the SWA to the cooker switch of suitable size for the installation.
Is there discrimination between the 32A breaker in the CU and the breaker for the sockets in the summer house.

Just seen Lenny's post yes you would need an upfront RCD 100mA typeS in the house.
 
Last edited:
So my best option is to install c.p.c from c.u. to primary of cooker switch side and and have the lot as pme ? leave the rod in as back up ? no utilitys present by the way
 

Reply to Not seen this before ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
There is nothing inherently wrong with this part of the layout. There is another option that you may want to consider. Those supply conductors...
Replies
3
Views
2K
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
831

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top