R

ratboymark

hello
got some jobs comming up replacing 6mm tails to 25mmm with 16mm earth all bonding is in place and meets regs but there is a good chance i wont be able to change the dis board witch is the re wireable fuses if i was to notify this i was thinking i would put on the eic that it was a alteration and client has been advised to upgrade distribution board do you think this would be the right way of doing it?
 
No requirement to change the board for that.
You should not be really giving advice on a Certificate, that is what a Report is for, and if you were to give written advice, you really should have indemnity insurance.
What you need to do is note under comments on existing installation any defects (where reasonable practicable) you have spotted.
In this case, you would note lack of RCD protection to socket-outlets intended for general use by ordinary persons.
Lack of RCD protection for socket-outlets for use by mobile equipment outdoors (if applicable).
Lack of additional protection for cables concealled in walls if appicable.
Lack of RCD protection for circuits of a location containing a bath or shower.
 
yep i think that would be the best way of doing it if i noted all the lack of rcd protection the ideal solution would be if they let me put a new dis board in with rcd protection what would be max disconetion time of a 100a fuse that the REC will of provided for my tails
 

Reply to Notifiable? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
815
  • Question
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight
2
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top