Araman

Having installed a new cu in a customers house I found the fan assisted oven (cooker only as the hob is gas powered and the cooker was fed through the ring main) was tripping the RCD constantly. There were no faults that I could find so I laid a dedicated radial to the cooker. This has very nearly cured the problem inasmuch as the RCD now trips only once about 5 minutes after the oven is switched on and thereafter never again.
The fan comes on as soon as the oven is switched on so it is not the motor starting up that is causing the RCD to trip.

I am happy enough to lay the radial from an independent non-RCD controlled supply which will end the problem. But do any of you out there know the answer to this? Where do you think the problem is? I know I comply with 17th edition by feeding the cooker through a FCU rather than a plug and socket but it would put my mind at rest if anyone knows the answer.
 
As Wirepuller has stated re the element breaking down.

The only problem is if you install a new radial non RCD cct will the cable run comply with the regs.

I would suggest a new element as it sounds like its breaking down especially when cold!!!

Sounds like your final ring circuit may also have a high leakage clamp the tails and see what the reading is!!!
 
It sounds tough but you can’t be held responsible for client’s crappie old oven.
If you do appliance repairs quote for repair
If you don’t inform them appliance is faulty & they should get it repaired at their cost
I would not down rate your circuit to non rcd .
I you have certificated your work & it is sound the responsibility lays with them an oven is a Portable tested bit of equipment normally classed as fixed or transportable.
 

Reply to Nuisance tripping RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
570
davesparks
D
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
419

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top