O
Octopus
Hi, I'm in the process of trying to eradicate nuisance tripping in a house and in the course of my fault finding I've discovered that the "ring" concerned is in fact 2 radials off one 32A MCB.
1 leg goes to one socket and tests confirm circuit is OK
The other leg feeds a total of 25 outlets (possibly more) and without ripping up their floors appears to have hidden junction boxes. The house has had at least 2 extensions - and the identified sockets (except spurs) all have 2 cables coming out of them so the radial doesn't appear to have an end or ends!
My issue is that I'm getting very poor IR readings on the "2nd" leg.
Any suggestions for speeding up the process to find the fault would be useful.
1 leg goes to one socket and tests confirm circuit is OK
The other leg feeds a total of 25 outlets (possibly more) and without ripping up their floors appears to have hidden junction boxes. The house has had at least 2 extensions - and the identified sockets (except spurs) all have 2 cables coming out of them so the radial doesn't appear to have an end or ends!
My issue is that I'm getting very poor IR readings on the "2nd" leg.
Any suggestions for speeding up the process to find the fault would be useful.