O

Octopus

Hi, I'm in the process of trying to eradicate nuisance tripping in a house and in the course of my fault finding I've discovered that the "ring" concerned is in fact 2 radials off one 32A MCB.

1 leg goes to one socket and tests confirm circuit is OK
The other leg feeds a total of 25 outlets (possibly more) and without ripping up their floors appears to have hidden junction boxes. The house has had at least 2 extensions - and the identified sockets (except spurs) all have 2 cables coming out of them so the radial doesn't appear to have an end or ends!

My issue is that I'm getting very poor IR readings on the "2nd" leg.

Any suggestions for speeding up the process to find the fault would be useful.
 
Disconect from cu and do end to end or r1+r2 and record results then the highest reading other than spures should be the last 2 points then see if there is 1 or 2 t&e in each if you got 2 you have a break in circuit somewhere between and would need to find it and reconnect the ring. If you are 100% sure it is 2 SAFE radials you need to connect to 2 seperate mcb's max 20A.
Paul
 
sorry just re read thread. You still need to do above to sort out circuit safety and then test 1/2 the circuit to find which half then 1/2 that ect untill you find where problem is. What are thr readings? are you sure nothing is plugged in? sure there are no neons ect?
Paul
 
paul, thanks for your thoughts.

The "bad" half has very low IR readings and due to the nature of the additions to the circuit thats why I'm a bit perplexed - purely because the "bad" half doesn't appear to have an end, or possibly 2 ends. Oh for x ray to see where the cables run to and from!

Have thought ahead and will be recommending 2 x 20 Amp circuits - fortunately the CU has 3 spare slots.
 
Is it in 2.5mm if so a radial should not have been put in on a 32A breaker. What i think is more likely is a damaged ring. - are the the two cables identical? I assume you have checked for continuity on r1, rN and r2.
Just a thought but i would have a good look for pictures hanging on nails directly above sockets or recently fitted dado and picture rails, curtain poles etc.
 
Yes, tests for continuity were almost the first thing I did and hence why I found that the ring is not a ring. The house has been extended twice and there are 3 types of 2.5mm cable in evidence.

As previously mentioned I have confirmed one leg as a radial and I "think" that the other is a radial with 2 loops on the end -got me and my mate scratching our heads yesterday.

Its not easy to explain but the home owner assures me they haven't done anything recently.

The house layout is not logical, parts of it date back at least 200 years, nor is the "hidden" routing of the cabling.

Looks like I'll be taking sockets off again, doing continuity tests and making notes again.
 
Last edited by a moderator:
Before you start ripping up boards start spliting the circuit up as they say split it in half if the half from the cu is fine then again split the second half and so on you should be able to track it down ie first 12 socket are fine the next 4 are ok but the next 4 have a fault and the last 5 are clear. To acertain if there is a joint box again split the circuit put your meter to bleep and connect accross N-E then get a plug top link out N-E then plug them in to each socket evertime you hear the bleep you know that socket is on the circuit. now if it was a pure radial then you would have a pair at each socket until you hit the last one but if there is tap offs via junction boxes then you need to track it down.
I had a problem with 3 room lights not having an earth and somebody was going to rip up floors to rewire I got a lead plugged it into a socket linked the earth to one of the lights switches and all 3 rooms now had an earth so I was asked what does that prove and I said well the circuits are ok but some fool has not put the link in between the earth connectors in the junction box
 
Last edited by a moderator:
Am I missing something - shouldn't all socket circuits be on a ring now (17th Ed.) unless just feeding one socket? You need to make those radials into a ring if they are radials.
 
when i rewire the house im buying to do up all my power circuits are going on 4mm Radials and will Be 32a RCBO as well!
10mm for 2x Showers and 1x cooker on 40A RCBO!
and 1.5 for lights on 6a RCBO

not messing about with rings and problems that they bring!
 
Last edited by a moderator:
when i rewire the house im buying to do up all my power circuits are going on 4mm Radials and will Be 32a RCBO as well!
10mm for 2x Showers and 1x cooker on 40A RCBO!
and 1.5 for lights on 6a RCBO

not messing about with rings and problems that they bring!

Fine sensible decisions Durham

You could even become the Uk representative to the EU on circuit design :)
You may become famous as the member without a ring :eek:
 
UPDATE:

Customer is having some major building work done so I decided to pay them a visit to see what would be revealed when they removed cladding hiding an old steel which is being replaced.

The builders have noticed that its now possible to see "outside" whilst looking at the inner wall of the "music" room. In this space is a conduit running down to a light switch and another running down to a socket. The customer had said that "horizontal rain" was the main problem - looks like they need some repointing done!
 

Reply to Nuisance Tripping, ring is 2 radials with loops! in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
Why aren't you asking them?
Replies
5
Views
783
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
Perfect!! Thanks a lot gents. You've been massive help this last day 😁
2
Replies
43
Views
5K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
447
davesparks
D
  • Question
Hi James. I agree that is a method of extending the ring which I have seen many times. However in this instance, the electrician who wired the...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks