rob69

Hi All,
I have got a nuisance tripping problem on a kitchen ring circuit with its own RCBO.This includes fridge/freezer,washing machine, cooker hood,microwave,stereo and kettle.The tripping happens very irregularly!!!!!!
Which item is most likely to cause this and for what reason??????
Also,is it worth getting a PAT test done on these appliances?????
Thanks Rob
 
could well be a cumulative thing with 2 or more appliances contributing some earth leakage. If it's possible it might be worth disconnecting one or more and trying to establish which one(s) are the culprits.
Anything with capacitors/ electronic circuitry could be one of the less obvious causes that just start to occur as the appliances age.
 
Do you have an RCD ramp test function on your meter?

If so, do a ramp test without any load on the circuit...then do a ramp test with each piece of equipment switched on...it might give you an indication of where the leakage is coming from.

Another method would be to use a clamp ammeter on the RCD ...this will need a suitable RCD with a good resolution however.

Yooj
 
I would agree with the accumulative leakage of all the appliances. As suggested ramp testing the RCBO with one appliance at a time plugged in will give you the best idea of which one is the biggest contributor.
 
If they have one of those kettles which fits onto a base with a socket, check for water being spilled into the base socket. I've traced occasional tripping on kitchen rings to this on several occasions.....including in my own gaff when the split load rcd tripped one christmas day !
 
If they have one of those kettles which fits onto a base with a socket, check for water being spilled into the base socket. I've traced occasional tripping on kitchen rings to this on several occasions.....including in my own gaff when the split load rcd tripped one christmas day !

Yep had this as well ! only a small leak then shook base unit and water dripped out. and a washing machine with mice damage to controll wiring ! also if washing machine elements get burnt out the chassis can become live !
 

Reply to Nuisance tripping in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
894

Similar threads

  • Question
Thats why somebody told you to spk to the sparky
2
Replies
18
Views
2K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top