If for whatever reason you can't do an R1+R2 test on a ring final circuit (unable to identify opposite legs). There's also an option on the paperwork for the R2 value...

Am I correct in thinking that you do an end to end test on the CPC's which would give you r2, then just divide it by 4 to give you R2?
 
If for whatever reason you can't do an R1+R2 test on a ring final circuit (unable to identify opposite legs). There's also an option on the paperwork for the R2 value...

Am I correct in thinking that you do an end to end test on the CPC's which would give you r2, then just divide it by 4 to give you R2?
Yes but what about your continuity tests end to ends on the ring final?
If it's periodic testing then just take the zs at each socket.
If it's initial verification then continuity needs to be established/verified so R1+R2 shouldn't be an issue.
 
Edit But yeah doing end to end on live and cpcs added and divide by 4 should give you total value of R1+R2 as you have 2 middles which can be considered the end of the circuit if it was a radial and 2 conductors in parallel
 
Following on from the above question consider a situation where you can't readily disconnect the cpc at any point to test it, or doing so is rendered largely pointless by the installation method.

I'm thinking of a circuit wired in SWA, MICC or steel conduit/trunking.
 

Reply to Obtaining R2 value on RFC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top