View the thread, titled "Obvious question on transformer calc" which is posted in UK Electrical Forum on Electricians Forums.
Spark2be
Calculating the voltage to be able to calculate the full load current of a 850kva 32kv/400v 3 phase transformer with 8% reactance:
400 x 8
100 = 32v
can some one explain this? It won't bloody sink in until I can see why I am 1. Multiplying the voltage by the reactance and 2. Dividing it by 100?? I know it will be simple to you guys...
thanks.
An 750kva 11kv/400v 3 phase transformer has a reactance of 5%. If a short circuit of negligible impedance occurs on the secondary while rated voltage is applied to the primary calculate the short circuit mva and the short circuit current.
I can remember and calculate the steps but what I am trying to do is understand each step and know why I am doing each step, if you know what I mean.
Thanks.
1. Find voltage to be able to calculate the full load current
400 x 5
100 = 20v
2. Normal full load current
400
20 = 20
3. Short circuit power
750000 x 20 = 15 mva
4. Short circuit current
15000000
400 = 37.5kva
now I think that's correct but I am having trouble with the particulars of steps 1 & 2.
thanks.
You need to calculate the transformers full load current and then divide by the reactance to give the maximum fault current.
This only holds good for a theoretical zero impedance source.
That should have read 37.5ka (not kva)
thanks for the advice Tony.
So is the answer to step 2 in amps?? Volts divided by volts = amps?? Apologies for being a bit dumb lol.
Transformer full load current = (P/3)/(U/√3)
Transformer maximum fault current = FLC/ reactance
I get ((850000/3)/(400/√3))/0.08 = 15.33KA
Reply to the thread, titled "Obvious question on transformer calc" which is posted in UK Electrical Forum on Electricians Forums.