K

Keef

Found a strange one at a golf club:

Supply to 2 x no 63 A sockets feeding 2 x temp portakabin supplies.

Fed in 3 core 10mm from a 3 pole isolator Brown = Line 1; Black = Line 2; Blue = N; Sheath = CPC

Goes to a box with the 2 x 63A sockets on with the neutral being split and the sheath isolated and an earth rod so the portakabins are TT about 3M away from sockets & earth rod combo. Before the isolator is 2 RCD's and 2 x 63A MCB's (1 per circuit).

Its a single phase incomer of 100A, there is no overload issue here and isolation for the cable seems to be in order.

Loading in cabins varies but portakabin 1 (office) has got 3 x 2kW heaters in and a water heater, portakabin 2 is lighting, heater and workshop type kit (drills, bench saws) equipment.

Its odd due to the neutral being split and what current is going to go down it as it is all single phase.

Info on how to calculate this and opinions please.
 
Imagine a 3 phase incomer to a property.
3 phases and Neutral all the same size conductors

2 phases fully loaded, 1 phase nothing.

Is the Neutral overloaded?
 
Imagine a 3 phase incomer to a property.
3 phases and Neutral all the same size conductors

2 phases fully loaded, 1 phase nothing.

Is the Neutral overloaded?

Yea that was my thoughts, but it just got me thinking (too much probably). As its single phase the chances are the neutral can get overloaded, but i need to calculate to be sure. I can never get into the office building (rented by someone else) to turn everything on and check so may need to rely on calculating it.
 
Imagine a 3 phase incomer to a property.
3 phases and Neutral all the same size conductors

2 phases fully loaded, 1 phase nothing.

Is the Neutral overloaded?

No, but that is entirely irrelevant as the question is about a single phase supply.

The neutral is carrying the combined neutral current from both 63A supplies.
 
Yea that was my thoughts, but it just got me thinking (too much probably). As its single phase the chances are the neutral can get overloaded, but i need to calculate to be sure. I can never get into the office building (rented by someone else) to turn everything on and check so may need to rely on calculating it.

Surely the answer is obvious?

The neutral currents will combine, giving you a potential 126A down that 10mm neutral, the 100A cutout fuse will happily let 126A flow for quite a while.

This is why the regulations don't allow for two circuits to share a neutral.
 
May I respectfully draw your attention to posts 1,3,4 and 8 Mr Tony sir, the installation appears to be of the single phase variety ;)

Now why doesn't this forum have that nice 'poking with a stick' smiley? You'll just have to imagine it for now.
 
Neutral currents on a poly-phase system aren’t cumulative

In = √((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))

u3y2yhyz.jpg
 
If I have interpreted your post correctly you have got two circuits ie fed from two separate OCPD's in one cable but sharing (borrowing) the same neutral. I would have thought the OCPD's would need to be two pole or linked so one trips both trip and giving one correct point of isolation.
 

Reply to Odd ball mains supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
757
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

  • Question
The rules on parallel conductors are very clear: same length, same OCPD, same terminations. That’s why there’s no other derate factors...
Replies
9
Views
974
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top